About fire extinguisher in crawl space

About fire extinguisher in crawl space

About fire extinguisher in crawl space

(OP)
Do we need to put fire extinghuishers in crawl space according to NFPA? it is only about 1 meter high inside. I think it is impossible for people running to get fire extinguisher in emergency.

RE: About fire extinguisher in crawl space

Is the building combustible or noncombustible construction?
Is the building required to be protected by an automatic sprinkler system?
What is the occupancy of the building?

RE: About fire extinguisher in crawl space

(OP)
The building is wood construction and is protected by sprinkler system even in crawl space. Office area on main floor and residential on 2nd and 3rd floor. But there is nothing in crawl space.

RE: About fire extinguisher in crawl space

Yes there is - wood. You have combustible construction. Sprinkler protection is required in the floor ceiling area of the 1st floor unless you can subdivided it in accordance with Chapter 8 of NFPA 13. I doubt if sprinklers are required in the residential portion of the building if your design is based on NFPA 13R.

RE: About fire extinguisher in crawl space

(OP)
Then How about fire extinguisher? I can not see the point of using it if the height of crawl space is low. But I have not found clear statement of "no need"

RE: About fire extinguisher in crawl space

Are you located in the US? Is your project subject to US design standards for fire protection systems?

RE: About fire extinguisher in crawl space

(OP)
In canada

RE: About fire extinguisher in crawl space

In Canada, all of the proviences adopt NFPA 13 and NFPA 13R. Read them. You must provide automatic sprinkler protection (not portable fire extinguishers) above the space on the 1st floor. It is a combustible space and the space of the 1st floor is residential.

You cannot get around the fire protection requirement unless the Canadian Building Code has some exception. I don't have a CBC.

If you are having problems applying the construction codes, seek professional design assistance from a licensed fire protection engineer.

RE: About fire extinguisher in crawl space

Take a look in NFPA 10 for locations.

I can't recall a requirement to put portable fire extinguishers in an attic that is sprinkled, so my gut feeling is why would they be required in a 3 ft crawlspace that is sprinkled?

Take the "V" out of HVAC and you are left with a HAC(k) job.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources