how to calculate the foundation for a 2 MW generator
2

how to calculate the foundation for a 2 MW generator

how to calculate the foundation for a 2 MW generator

(OP)
I´m trying to define the foundation for a 2 MW syncronous generator, and I don´t know how to calculate the next things maybe someone of you could help me....
  How can I calculate the short circuit torque and how to use it for the calculation of the foundation... this is a horizontal hydro unit with francis runner....
  What is the best option: double T asembly or a piece of metal mechanized with the holes for the bolts of the generator??
   sorry for my badly english and I hope to get some help from you... I´m just trying to know how to know how to do it

         thanks in advance

RE: how to calculate the foundation for a 2 MW generator

We would need the speed of the generator (or the number of poles) and is it 50 or 60 Hz

RE: how to calculate the foundation for a 2 MW generator

(OP)
ohhh, sorry.. yes I imagine you will need speed...  
1000 rpm....
 when I write it, I was thinking in get some formula .... or explanation...
    I hope someone could help me... I´m new on this mechanical things

RE: how to calculate the foundation for a 2 MW generator

(OP)
and the frequency is 50 hzm, this is Europe (Spain)

RE: how to calculate the foundation for a 2 MW generator

2 MW = 1.47x10^6 lb-ft/sec

1000 RPM = 105 Rad/sec

T=P/w = 1.47x10^6/105 = 14,000 lb-ft of torque

RE: how to calculate the foundation for a 2 MW generator

You need to get a structural engineer to do this for you.

RE: how to calculate the foundation for a 2 MW generator

(OP)
yes, I´d contacted with a structural engineer but I want to know something about it... to discuss with him or understand what he explain me...
  other question, does somebody knows how to translate lb-ft to kg-metre.
  Ah, other question, Sreid, how you get the numbers for the formula
2 MW = 1.47x10^6 lb-ft/sec
  why you say 2 MW that valium

   thanks in advance to all of you

RE: how to calculate the foundation for a 2 MW generator


Power (lb-ft/sec) = Watts/(746 Watts/HP)X 550 lb-ft/sec/HP

I hate Kg-m as a torque unit.  How about Newton-Meter?

RE: how to calculate the foundation for a 2 MW generator

I don't know much about foundations.  For smaller machinery a thumbrule is 5 times the mass of the machine.

Note that the torque calculated above was the full load  torque.  You asked about short circuit torque... I'm not sure how one would calculate that.

=====================================
Eng-tips forums: The best place on the web for engineering discussions.

RE: how to calculate the foundation for a 2 MW generator

(OP)
   yes, normally the shrot circuit torque is 6 times the full load torque... or as long I remember...

   thank to everybody for the attention

   and thank sreid for your help, why you hate kg m??

RE: how to calculate the foundation for a 2 MW generator

Torque is power times angular velocity, and since the power goes way down during a short circuit, there is no way that short circuit torque could be 6 times full load torque.  The problem you're going to have during a fault is that the generator is going to overspeed and your foundation will have to deal with that.

RE: how to calculate the foundation for a 2 MW generator

181273,

Kilogram is properly a mass unit but torque is a force x length unit.  I know that Kg Force is a legitament unit of force but I think it creates confusion and leads to mistakes.

RE: how to calculate the foundation for a 2 MW generator

The short circuit torque can be calculted apprximately from the generator reactances, if you have x"d and X2. i have seen short cct torques as high as 10-12 times flt.

You also need the distance between the holding down bolt holes. ie width across the feet.

Regards

RE: how to calculate the foundation for a 2 MW generator

Good point.  cct = critical clearing time?

I'm remembering that case we are talking about a transient where the generator swings against the system.  The power is
P= E1*E2*sin(delta)/X

The max possible torque would be where delta approaches 90.  I can imagine that would be many times full load torque.  Protective relaying should disconnect the generator before it gets there.  

Out of phase closing might create torques close to that same maximum.

In the specific case of short circuit, there are large forces on the conductors but as David says I don't think necessarily large torques.

=====================================
Eng-tips forums: The best place on the web for engineering discussions.

RE: how to calculate the foundation for a 2 MW generator

Pete
cct = circuit, sorry for the confusion.

The short circuit does cause a large torque, albeit only for a few cycles.

Typically:
3 phase short circuit 2 - 5 x FLT
Line to Line short circuit 5 - 9 x FLT
An out of phase synchronism, 180 degrees out, up to 12xFLT.

An out of phase synch is unlikely, so designers ignore that possibility and normally quote the line to line as the worst case.

My little black book gives an approximation to the fault torque as:
1+ (3/2 x (sqrt3)x V^2/(x"d+x2))

So for x"d of 0.18pu and x2 of .2 gives 7.8 x FLT at 100% line volts.

Hope i havent confused you further!
richard

RE: how to calculate the foundation for a 2 MW generator

motorspert, could you kindly explain how torque could go up during a short circuit when power goes down dramatically and speed doesn't change much?

RE: how to calculate the foundation for a 2 MW generator

Is not the biggest hit the accidental way-out-of-phase paralleling?  Isn't that when the rotor lands out in the parking lot?

Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com

RE: how to calculate the foundation for a 2 MW generator

Keith, yep, bad paralleling is going to produce the highest possible torques, so high that mountings are not generally designed to withstand them.

RE: how to calculate the foundation for a 2 MW generator

(OP)
hi, and thanks for the reply to everybody.... specially motorspert... I got a little question...
"So for x"d of 0.18pu and x2 of .2 " you talk of two reactances...what´s is the name of this reactances???

   thanks in advance

RE: how to calculate the foundation for a 2 MW generator

x''d is the subtransient reactance and x2 is the negative sequence reactance, often very close in value to x''d.

RE: how to calculate the foundation for a 2 MW generator

Davidbeach,
Torque is only really power for a continuous period. During the very short time of a short circuit the stored magnetic energy disipates in any way it can generates high currents in the stator. These currents create magnetic fields which cause the rotor to accelerate or decelarate which is seen as an accelerating torque.  These torques occur for a very short time so there is no useful power produced.

Regards

RE: how to calculate the foundation for a 2 MW generator

Then you are defining torque as something other than Power over angular velocity.

Prior to the fault the mechanical torque in is equal to the electrical power out divided by the angular velocity plus losses.  Immediately after the fault the mechanical torque is unchanged, the electrical power out has fallen drastically, and the losses remain unchanged.  In the short time following the fault, the mechanical power remains unchanged, the electrical power remains at the lower level and the power imbalance causes the shaft to accelerate.  As the shaft accelerates the angular velocity goes up, therefore the mechanical torque in goes down.  No increase in torque following a fault so long as torque is defined as power divided by angular velocity.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources