overhead conductors used for 400/230 V circuits

overhead conductors used for 400/230 V circuits

overhead conductors used for 400/230 V circuits

(OP)
What size conductors would one use for the secondary mains on a 400/230 V system?  The three-phase supply transformer is 315 kVA.  The application is for a western African country.

RE: overhead conductors used for 400/230 V circuits

What size do you calculate?

RE: overhead conductors used for 400/230 V circuits

(OP)
I'd probably use something like 477 Al.  This is my initial cut at it based on ultimate full load of 455 amps.  I still have to look at the voltage profile and circuit lengths to see if that's OK.

What I meant to say was what are the standard metric sizes in mm-squared that are used in this area?  Or could you point me to a conversion table from AWG to metric.

RE: overhead conductors used for 400/230 V circuits

Look at table 8 in the back of the NEC, it gives mm2 values for all the common AWG sizes.  What might be available could be an entirely different matter.

RE: overhead conductors used for 400/230 V circuits

If you are sizing your equipment for 477 amps you would need a 600 amp service. The rating for 350 cu is 310 amps. A parallel service of 2 #350's = 620 amps. The rating for 500 kcm AL is 310 amps. Two per phase = 620 amps.

RE: overhead conductors used for 400/230 V circuits

I just realized you post was for Overhead Conductors. I found information at this site http://www.cable.alcan.com/NR/rdonlyres/97F54474-BC52-4D63-8092-84CA52D610E9/0/multiplexoverhead.pdf

I think you may have some problems due to the weight of the cable.
2/0 4C   649 lbs/1000ft  210 amps
3/0 4C   801 lbs/1000ft  240 amps
4/0 4C   991 lbs/1000ft  280 amps
336 4C  1591 lbs/1000ft  330 amps

If your load is 455 amps, you would require 2 - 3/0 cables.
What is the estimated distance for the installation?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources