Earth leakage trip during lightning
Is it normal for a domestic 220V 30mA earthleakage unit to trip during a lightning storm? I have experienced problem this on numerous occasions.
RE: Earth leakage trip during lightning
It is only 'normal' if you have an insulation problem somewhere in your system - It sounds like an earth potential rise problem.  Is your area PME or MEN?
Are you refering to a GFCI device when you say earth leakage unit?<\b>
The complaint can show up where the LV circuit is served from a Grounded-Wye Primary/Grounded-Wye Secondary distribution transformer.  Steep-rise-time zero-sequence currents are reflected in both sides of the transformer's common metallic hi- and low-side connection.  IIRC, the high- and low-side currents in grounding-electrode conductors may be [not necessarily equally] divided between the two.
For lightning hits, 30 mA is a relatively low value.  Isolation of the high-side neutral-to-ground connection may cure the problem, but for graded-primary insulation {or singe-bushing transformers,} the cure may be worse than the symptom.