Hi,
Could anyone tell me why does induction generators, like those installed on wind turbines,draw large reactive currents following a fault at its terminal ?
Thanks in advance.
Could anyone tell me why does induction generators, like those installed on wind turbines,draw large reactive currents following a fault at its terminal ?
Thanks in advance.






RE: reactive current inrush on induction generators
Power factor of faults is usually very low meaning there will be a lot of reactive power required. This is nearly always true and is not unique to induction generators.
Induction generators in normal operation require a lot of reactive power for excitation.
RE: reactive current inrush on induction generators
My question was of course large reactive currents of induction generators during faults. I just read in a paper that in some cases, caps are unable to support reactive power requirement of induction generators during faults. So dpc, you said that power factor is very low during a fault, isn't there a physical explanation to that ?
RE: reactive current inrush on induction generators
Actually, the load impedance is still there, but it is being shunted by the fault.
I think the paper may have been referring to external faults, not faults in the generator.
Induction generators will never be able to provide reactive power - they consume reactive power.
RE: reactive current inrush on induction generators
RE: reactive current inrush on induction generators
RE: reactive current inrush on induction generators
RE: reactive current inrush on induction generators
If the synchronous generator gets its excitation power from the ac mains (such as with a static exciter), it can also experience voltage collapse for very close faults.
RE: reactive current inrush on induction generators