Do you guys have good information on sizing thermowells (U length)? I am looking for something to help with spec'ing out some themowells. This is a new area for me and would appreciate any help that you could give. Is there any chart that basically gives U lengths for just about all possible combinations of piping and accessories? Not sure if there is something out there like that, but worth asking. Thanks!





RE: Thermowells
Try http://
or
http:
The U length depends on your process requirements. Typically, for tanks and vessels, we specify the length between 6-8 inches inside the vessel. Be careful on interference with equipment inside the tanks though, such as heating/cooling coils, etc. Thermowells for piping can be a bit trickier.
______________________________________________________________________________
This is normally the space where people post something insightful.
RE: Thermowells
It is reasonably common for small piping to put the well in one side of a tee and let it protrude upstream a ways. That way you can put a 6" or 8" well in a 1" pipe.... Then the tee drains through the common port.
RE: Thermowells
RE: Thermowells
RE: Thermowells
For inside tanks, usually 6-8 inches off the wall is sufficient to get away from wall effects.
For pipes, usually to mid-line for pipes 4" and under. For 4" and larger, usually 1/4 D is enough. When you get really big, 10" and larger, a flow regime/character study may be needed to determine where exactly the well needs to be to get the reading that is representative of whatever you are trying to measure.
"Do not worry about your problems with mathematics, I assure you mine are far greater."
Albert Einstein
Have you read FAQ731-376: Eng-Tips.com Forum Policies to make the best use of Eng-Tips Forums?
RE: Thermowells
RE: Thermowells
As most wells these days are flanged, consider a flanged well. The pipe extension (top of pipe to flange face) may be six inches. Frequently the calculation will eliminate a 12-inch insertion length. I try to select thermowell insertion lengths for any temperature element that would match with dial thermometer stem lengths. A 10-inch "U" on a flanged well should match a 12-inch stem. This would be the longest well to consider in most piping cases. This issue is not a problem for vessels.
Consider wells that fit the following pattern except that threaded wells on insulated lines may require longer lag extensions.
Stem lengths in inches:
Stem, "U" NPT "U" Flanged
2.5, 1"
4, 2.5" 2"
6, 4.5 4"
9, 7.5" 7"
12, 10.5" 10"