Hello.
I have a question concerning Safety Relief Valve coefficients of discharge (Kd).  Consider a case where an ASME stamped safety relief valve (for a Sec. VIII, Div. I application) is installed with liquid trim.  Assume the conventional safety relief valve has a Kd value of 0.7 for this liquid trim. Also assume the same safety relief valve has a gas/vapor Kd value of 0.9 when installed with gas/vapor trim. My question is if one is to now consider a sizing case for all vapor relief, what Kd value would you use for this safety relief valve since it is installed with liquid trim? 0.9 or 0.7?  A similar case would be just the opposite, where an existing SRV is installed with gas/vapor trim and is subject to all liquid relief.  Is the Kd value a function of the installed trim?  Thanks in advance for any help.

RE: Coefficient of Discharge for Safety Relief Valve Sizing

Hi,

For preliminary sizing you can use Kd=0,65

RE: Coefficient of Discharge for Safety Relief Valve Sizing

For the vapor only case, use Kd = 0.9 and calculate the minimum required area, Avapor.

Compare this to the documentation of the current worst case scenario.  There should be a minimum required area, Aliquid, calculated for that.

If Avapor > Aliquid, the worst case scenario changed and you must change the trim.  If Aliquid > Avapor, the liquid case is still the worst case scenario and don't change the trim.

If you had a 2-phase flow scenario, you'd use Kd = 0.9 for that and calculate A2-phase.  The largest required area of the three flow phases will determine the size and trim of the relief device.

Good luck,
Latexman

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources