Steel beam and metal deck unbraced length
Steel beam and metal deck unbraced length
(OP)
I have a concrete slab supported on a secondary steel beam. The structural drawings that I have are not the final construction drawings. They do not show any studs or how the metal deck is attached to the steel beam. Now, as per " Fundamentals of Beam Bracing" by Joseph Yura "a cross member merely resting (not positevely attached) on the top flange can significantly increase the lateral buckling capacity. The restoring solution is sensitive to the initial shape of the cross section and location of the load point on the flange. Because of these difficulties, it is recommended that the restoring effect not be considered in design". My question is the following, Can deck puddle welds be assumed as the possitively attachment points and by doing so, can I develop the continuos lateral support of the beam to develope the full capacity of the section?






RE: Steel beam and metal deck unbraced length
Without going back and finding that paragraph by Yura, I think he's talking about a situation like a conc slab just simply sitting on the steel beam top flange. In that case, if the beam starts to twist, the slab will be pushing down on the flange tip that's going up, providing a torsional restraint of sorts. Note that you only have to restrain twist OR lateral movement of the compression flange. I don't think that's what you have.
RE: Steel beam and metal deck unbraced length
I think you are correct. I'll have to consider the puddle weld as providing lateral restraint to the top flange. Thanks!!
RE: Steel beam and metal deck unbraced length
The only time this makes me nervous is if I have a roof deck only and am trying to brace a girder. With the deck flutes running parallel to the girder, it's not as obviously providing a lateral brace.
RE: Steel beam and metal deck unbraced length
Would you ever consider deck with the flutes parallel to the beam to brace the beam? I have only used the beams that the deck is spanning to as bracing the girder. Assuming it is deck only as you say above.
RE: Steel beam and metal deck unbraced length
OTOH, it might be completely irrational to not use the deck. The brace force and stiffness is very tiny for a continuous top flange brace. It would take some effort to quantify the resistance, so I'd probably never try to prove that it's adequate.
RE: Steel beam and metal deck unbraced length
The gist is that I would not assume that it braces the beam.
RE: Steel beam and metal deck unbraced length
RE: Steel beam and metal deck unbraced length
RE: Steel beam and metal deck unbraced length
Nethercot did a lot of work on this in the 70's, however the most up to date paper I am aware of is by Helwig and Frank entitled "Stiffness Requirements for Diaphragm Bracing of Beams" which was published in the Journal of Structural Engineering, November 1999. It is a well written and informative piece.
What you have to keep in mind is that it is the DIAPHRAGM action of the deck that is bracing the top flange, not the actual bending of the deck (though this does contribute some it is actually negligable compared to the diaphragm stiffness component). For the beam to fail in a lateral torsional buckling mode, the top flange has to translate laterally. The diaphragm stiffness resists this lateral translation. Diaphragm stiffness (the G' term in deck catalogs) is determined irrespective of the direction of the deck span. It is based on fastening schedules and length of deck span.
The basic finding of the paper is that the shear modulus (G') required for a deck to brace a beam for an applied moment Mu is equal to:
G'required = (Mu-Mg)/[(tributary width of deck)(0.375)(d)]
Where Mu is the applied load, Mg is the unbraced moment strength of the beam, tributary width of deck is the beam spacing, 0.375 accounts for top flange loading, and d is the depth of the beam. Make sure all your units work out.
What I have found is that the G' required to develop the full plastic moment strength of beams in most general cases is easily provided by typical 2 and 3" composite deck profiles - again irrespective of flute direction.
RE: Steel beam and metal deck unbraced length
RE: Steel beam and metal deck unbraced length
I just read through some of that paper and I am just wondering if it is assuming that locally there is not going to be a problem:
"The metal forms can provide lateral bracing to the top flange of the beams or girders on which they are fastened due to the forms large in-plane shear stiffness."
Another example is how many engineers provide cross bracing adjacent to cmu walls when the deck is running parallel to the wall, instead of just relying on the deck as bracing. Althought there is a tremendous diaphragm shear capacity in that direction, I am wondering if locally it has to be able to get into the diaphragm first.
I emailed the engineer that told me of the collapse I mentioned for more details. He is also a professor that owned his own company for 30 years. Perhaps I misunderstood something when he told me about that collapse.
RE: Steel beam and metal deck unbraced length
"Beam elements with only out-of-plane stiffness
were used along the edges of each panel to prevent local diaphragm distortions. The out-of-plane moment of inertia of the stiffening beams was of the same order of magnitude as the
corrugations in the actual deck panels."
RE: Steel beam and metal deck unbraced length
1. I'm not sure of your thought here. The sentence you reference summarizes the whole paper.
2. Engineers do a lot of things that might not technically be necessary but are considered good practice. I would probably put in bracing in that situation too. I will be ineterested to here more about the failure you are referring to.
3. I do not believe the FE modeling was based on flutes perpendicular to the beams - it was meant to be general and applicable to different deck profiles irrespective of direction. They used essentially just a fake flat surface and varied values of "E" to provide G' values similiar to those from actual deck profiles (read the paragraph after the one you referenced regarding the beam elements). Those little beam elements were just put in to prevent this flat surface from erroniously experiencing plate buckling. They chose to use a moment of inertia equal to "the same order of magnitude" as the corrugations just to have something within the ballpark to prevent this plate buckling. It is my understanding that these beams were placed around all four sides of each FE panel.
RE: Steel beam and metal deck unbraced length
RE: Steel beam and metal deck unbraced length
RE: Steel beam and metal deck unbraced length
"You are correct. Deck parallel to a girder flange does not brace the girder flange. Take the brace force required of the girder flange, 4% of flange force, and apply it as a load to the edge of the deck 20 - 22 ga deck and see that the deck cannot possibly take it in compression"
RE: Steel beam and metal deck unbraced length
The required brace force should be spread over a fair portion of the beam, so might not be all that much.
It would be an interesting 3-4 hour task to create a beam and portion of deck using shell elements, give the beam an initial out-of-plumbness so it will try to roll, and then apply load.
RE: Steel beam and metal deck unbraced length
RE: Steel beam and metal deck unbraced length
I have a spandrel beam parallel to the deck flutes, can the deck brace the top flange of the beam?
In that case, if the top flange tries to buckle toward the inside of the bldg, then the deck goes into compression. You or I could probably put on a pair of gloves and manually bend/buckle the deck in this condition. It would be a lot stiffer and stronger at an interior beam.
BTW, I'm inclined to not use it also, but I doubt I can prove that it's always wrong to use it.
RE: Steel beam and metal deck unbraced length
Second, the whole previous justification in the replies above was that the diaphragm takes the load, now you are saying it is ok as long as it is not a spandrel beam?
RE: Steel beam and metal deck unbraced length
I wouldn't use the deck to brace the beam, but I think the forces might be small enough that one could get away with it at interior beams.
Somebody else brought up the diaphragm stuff. Right or wrong, I don't think of this as a diaphragm strength and stiffness issue. I can see how the deck would bend/buckle locally enough to let the top flange translate a little. As with any stability bracing problem, once the member starts buckling, the required brace force shoots way up.
RE: Steel beam and metal deck unbraced length
RE: Steel beam and metal deck unbraced length
"I would not want to count on the deck for lateral bracing in the direction you are considering."
RE: Steel beam and metal deck unbraced length
I will admit I always used to assume a beam is braced whether the deck was parallel or perpendicular to the beam or girder as does the other engineers that I know. It seems to me that if you can assume a cmu or tilt wall is braced continuously by a roof deck with flutes running parallel along the top of the wall, then you should be able to assume a beam is braced also. Would you consider the same wall braced at the top if there were no joists or beams framing into the wall and the wall had to rely solely on the strength of the parallel flutes along its entire segmented length? Or would you put in additional cross bridging as I have seen done many times to help brace the top of the wall?
However, I am having a problem finding a research document that justifies this and addresses any local buckling of the deck that might occur in the immediate area of the beam. I think for 99% of the beams that go up, the force to brace the beam is low enough to assume the parallel deck is adequate for bracing, but I am only about 85% sure of this.
I have a situation now where there are roof beams along the edge with 3" long spanning deck running parallel
RE: Steel beam and metal deck unbraced length
"During concrete placement, because the deck is parallel to the beam, the beam will not have continuous lateral support. It will be braced, at 10ft on center by the intermediate beams."
I am not saying this is all encompassing. The floor deck in the example he speaking of is 3" composite metal deck.