Missing winding
2

Missing winding

Missing winding

(OP)
I have a motor that is running on 3 ph 240 volt.
I went to switch it to 3 ph 480 and found it would not run.
After checking each winding I found from 1 to 4 is open.
I put it back to the 240 and it runs.
Why is this and what is it doing to this motor?

RE: Missing winding

For 240 V, the windings are in parallel.  For 480 V the windings are in series.  So with 1-4 open, at 240 V one phase is "Half open" but the phase is still there. At 480 V the phase is open circuit and the motor won't start because it is "single phasing" (one phase not operating) (but it pulls a lot of current).  

RE: Missing winding

What Sreid explained is the reason the motor still spins while connected in parallel ( 240), however it does not mean it is 100% good, the phase currents must be unbalanced generating a considerable negative sequence which traduces in lower torque and rotor overheating.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources