NFPA 12 . CO2 quantity

NFPA 12 . CO2 quantity

NFPA 12 . CO2 quantity

(OP)

Hallo all,
According to NFPA 12 How much quantity of CO2 is neacessary to protect dry electrical hazards. How should i calculate, approxmately?

Thank you for replys.

RE: NFPA 12 . CO2 quantity

It´s alittle late but, is it a total flooding system in a closed volume?.

RE: NFPA 12 . CO2 quantity

(OP)
Yes.

RE: NFPA 12 . CO2 quantity

Ok. NFPA 12 requires a inicial extinguishing concentration delivered in a quick way and then a 2nd application to prevent reignition that must be kept for some time. For example we bought a CO2 system for a electric generator (hydroelectric power plant) from a company and the design basis for this case was:


Initial extinguishing: The volume of the enclosure multiplied by a required extinguishing density (V=95m3, dens=1.3kg/m3 on 1 minute, mCO2=124kg). That lead to 3 bottles of 45kg of CO2 (135kg). Some people subtract the equipment included in the protected volume others don´t depending on the design concentration and other considerations or some add security factors.

There is a table in NFPA especial for electric rotating equipment that indicates the required kg of CO2 for the extended 20 min concentration. That lead to a quantity of 5 x 45kg botles.

So the system required 8 x 45kg botles, 3+5 that delivers CO2 with independent valve and pipe systems, one after the other.

Also, in our case we have two generator pits so the system was designed with a second 8 botles set as a back up battery.

This is just an example of the calculation included in the contract, but of course the correct aproach for each case must be designed by an expert due to the high risk of CO2 systems, type of fire/fuel expected, etc.

I know a person that have been involved in a CO2 accident and one guy almost die. This a serious matter.

One thing that I can critizice of  NFPA 12 (almost for the 2003 NFC edition) is that the security signs and other security provisions have not been standarized jet as I would like.

I can read on the 2003 ed, that it is too open, the security provitions mentioned some are too tight and others too soft, at least I would like to see an appendix on NFPA 12 given more criteria on this for different aplications. If somebody knows more about the current edition, please tell.

RE: NFPA 12 . CO2 quantity

(OP)
Thank you Devid for your detail explanation. Very helpful.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources