I was trying to find out the fault current capacity of 1/0 copper, 2/0 copper, 4/0 copper @ 30 cycles. For the use of choosing the right personal protective grounding equipment.
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Fault Current Capacity
RE: Fault Current Capacity
I'd recommend buying complete grounding sets from A.B. Chance or similar (if you're in the US). These will have a tested and published rating consistent with IEEE standards for safety grounds.
RE: Fault Current Capacity
http://
RE: Fault Current Capacity
2/0 - 20kA - 30 Cycles
4/0 - 30kA - 30 Cycles
But DPC is right, the clamps are usually the limiting component, buy a full set that is tested and rated for your application.