When making HVAC duct layout, do I need to specify volume control damper in branch duct if ceiling supply diffuser has the opposed blade damper?

Otherwise, having VCD in branch duct, shall I specify ceiling supply diffuser without OBD?

Please advise.

thank you.

RE: Volume Control Damper and Ceiling Register

If you want to reduce noise in the space, delete the diffuser/air terminal damper, and use only the branch duct balancing damper, which should be located at least 2 meters (7 feet) back from the air outlet.  The neck dampers and opposed blade dampers at the air supply terminal are just noise-makers.

Washrooms and un-occupied type spaces (storage rooms) would be fine with a terminal damper.

RE: Volume Control Damper and Ceiling Register

There is no way you can properly balance a duct system unless you install volume dampers on the branch ducts in a constant volume system. Trying to balance with just ceiling diffusers is asking for trouble as noise would be a critical factor

RE: Volume Control Damper and Ceiling Register

(OP)
Hi GMcD and imok2, Thank you very much for your reply.

RE: Volume Control Damper and Ceiling Register

Just as a note.  For a VAV system you do not need balancing (volume) dampers upstream of the VAV boxes.  Also I would still require the OBD at the diffusers.  This allows you to fine tune the system.

RE: Volume Control Damper and Ceiling Register

Further note to WilliamsGA response, if you have a crappy VVT system you would still require a balancing/volume damper upstream of the box.

I agree with the opposed blade dampers at the diffuser for fine tuning only.

RE: Volume Control Damper and Ceiling Register

why is it required for VVT?

RE: Volume Control Damper and Ceiling Register

Some of the VVT dampers/boxes that I have come across are pretty flimsy (not all though) and these systems do not always control properly without the balancing damper.  It could be the one bad installation from my experience, but I have since put balancing dampers ahead of the VVT units.

RE: Volume Control Damper and Ceiling Register

Having done TAB, I've found diffuser mounted OBDs to be consistantly problematic ( noise, impropoer diffuser neck velocity, and flow turbulance). A quality volume damper (with a low leak dial regulator, spring lock bearing, end bearing)located properly in the branch duct serving the diffuser should be more than adequate for air balancing purposes.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources