Header beam for a masonry penetration
Header beam for a masonry penetration
(OP)
I'm putting an addition on the back of a house that was built with exterior cmu walls. The new addition calls for the existing rear french door to be removed and the opening increased to 8 ft. Is there any reason that an LVL header cannot be used to support the masonry wall above? This wall effectively becomes an interior bearing wall with no possibility of moisture content becoming an issue with the LVL.





RE: Header beam for a masonry penetration
RE: Header beam for a masonry penetration
RE: Header beam for a masonry penetration
Where I am, they have allowed this condition if a lintel is attached to an LVL even though the wood beam is actaully carrying the lintel and most of the load.
In a truly hot fire - metal beams will often fail before heavy thick wood beams which simply char.
You might try an assembly using a steel plate on top of the LVL and see if that flies??
If not - you are probably stuck with angles under each side of the masonry.
Good Luck
RE: Header beam for a masonry penetration
Use a 16" deep masonry lintel (16" deep lintel block or a lower bond beam and the next course filled at the same time) to support the wall above. To build the lintel, use temporary shoring. Build the wall above. You will have enough height in the second floor wall to achieve arch action, which reduces loads on the lintel significantly. Make sure you have a bond beam for bearing and continuity at the top of the second floor wall.
If you are extremely concerned, you could go to a 24" deep lintel, but that could be counter-productive and a little messy depending on the details.
It is difficult to beat the continuity of construction and similar materials. Dissimilar materials lead to too many difficult situations as the building ages.
RE: Header beam for a masonry penetration
RE: Header beam for a masonry penetration
How would you support the ends of a LVL anyway?
Easiest is to use an angle each side of the wall.
RE: Header beam for a masonry penetration
"Wood members shall not be used to permanently support the dead load of any masonry or concrete"
8 foot is a long span for angles. Although it can be done, just we're at the upper limit for angle.
The best way to do this in a multi-wythe wall is with (2)
W8 beams (4 inch flange)W8x10 or 13. Insert in one face at a time. In other words, create opening in outer wythe, insert beam, then repeat in inner wythe. This is a good detail for exsiting walls, where temp shoring cannot be used or is impractical.
RE: Header beam for a masonry penetration
If your going to do this, put 5/16" plate needles throught the wall in the mortar bed just above the new lintel. Support these with a shore at each end.
With the wall above supported, install the new lintels directly under and cut off the end of the needles once you remove the shoring. Weld remainder of needles to top of beams for restraint.
regards
Csd
RE: Header beam for a masonry penetration
2006 IRC, R703.7.3: "Veneer above openings shall be supported on lintels of noncombustible materials . . ."
RE: Header beam for a masonry penetration