(OP)
what diversity would i use in this rm for the equip.there is a sm. ups rated at 1050watts ,and one at 980 watts..and some other equip at 1500 watts.. i am trying not to put in ac and just use a exhaust fan with a louvered door

RE: telecom rm

What delta temperature (temp inside room & temp outside)are you designing for??

RE: telecom rm

(OP)
the room is located in a climate controled bldg.. so if i was to exhaust it i would be pulling in lets say 78 degrees ,witha delta of probality on 20 to 25 degs

RE: telecom rm

Your UPS modules should be about 90% efficient or better: under normal conditions they are converting input power, conditioning it, and supplying the load; they don't actually consume much power under normal conditions. Losses will go up, sometimes significantly, when the unit is running from battery. They will remain higher than normal until the battery recharges.

Consider what happens to the cooling when the power fails: the UPS and loads will still be dumping heat into the room. How long does the UPS have to run? I am asking because I am often frustrated by the omission in many building designs of any provision to provide cooling for the UPS and loads once the mains fails. A top-of-the-line UPS is is useless once it shuts down on thermal overload!
 

----------------------------------
  Sometimes I only open my mouth to swap feet...

RE: telecom rm

Check the heat output from the UPS manufacturer instead of guessing.  They will all have their data available for your use.

RE: telecom rm

If you do proceed with exhausting the telecom room instead of cooling it, remember to exhaust more CFM than what is required to cool the room at 55F. This is because the air in the room will be transferred in from another space and therefore is warmer.

A green thought..."We don't inherit the earth from our ancestors, we borrow it from our children." (unknown)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources