telecom rm
telecom rm
(OP)
what diversity would i use in this rm for the equip.there is a sm. ups rated at 1050watts ,and one at 980 watts..and some other equip at 1500 watts.. i am trying not to put in ac and just use a exhaust fan with a louvered door





RE: telecom rm
RE: telecom rm
RE: telecom rm
Consider what happens to the cooling when the power fails: the UPS and loads will still be dumping heat into the room. How long does the UPS have to run? I am asking because I am often frustrated by the omission in many building designs of any provision to provide cooling for the UPS and loads once the mains fails. A top-of-the-line UPS is is useless once it shuts down on thermal overload!
----------------------------------
Sometimes I only open my mouth to swap feet...
RE: telecom rm
RE: telecom rm