Analog scale conversions

Analog scale conversions

Analog scale conversions

(OP)
Presently, I input a 4-20 mA signal into my DCS which represents 0 to 700 MW. I need to retransmit that signal over a communication data link as -700 MW to +700 MW. How is this accomplished?  Can someone please describe the SAMA logic which would represent this signal conversion?

RE: Analog scale conversions

I wasn't awary SAMA did comm protocol standards, but if your signal is 0-700 whatevers then the sign bit is always positive, right?  Is the comm protocol more complex than dealing with a sign bit?

Dan

RE: Analog scale conversions

(OP)
Dan, the SAMA logic does not involve the comm link. I need to make the change to the SAMA logic as a way of informing the DCS vendor the particulars of the logic change. My real confusion is the scaling. If 4 mA is 0 MW and 20 mA is 700 MW then how does one develop a scale factor when the process range becomes -700 to +700?

RE: Analog scale conversions

I don't use SAMA diagrams.  Consider showing a bias [ + / - ] station.  Next to the symbol write "input = 0-700 MW; output = -700 to +700 MW".

RE: Analog scale conversions

Not sure if your question is making any sense, but all you need to do is:

(current-4ma)*700W/16ma

That should be the conversion factor and you actually would not have any negative values as results, since all your inputs are, by definition, positive.

TTFN

FAQ731-376: Eng-Tips.com Forum Policies


RE: Analog scale conversions

I think the SAMA block you are looking for is a gain-bias - might be shown as K-Bias or K+B in the bloack diagram - which will have two parameters: parameter 1 is the gain (2 in your case) and parameter 2 is the bias (-700 in your case).
 

----------------------------------
  Sometimes I only open my mouth to swap feet...

RE: Analog scale conversions

What you are asking is this

You want to make 0% to be 50% and 100% to be 100% so...

Multiply by .5 and add 50%, now your range is -100% to 100% (-700 - +700MW) 4mA = 0MW (50%), 20mA= 700MW (100%)

Is this what you mean, or do you want the actual Sama symbols for adder and multipier too?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources