Can you specify SC connection if the bolts are subjected to tension? For example hanger connection?
Thanks

RE: Slip Critical Connection

Sure, but there's really no need unless they are also subject to shear.

RE: Slip Critical Connection

Yes.  There is a separate equation in the AISC specification to check for slip critical bolts with applied tension.

Are the bolts only under tension, as in there is no shear on them?  If so, why would you call out a slip critical connection?

RE: Slip Critical Connection

(OP)
The bolts under both tension and shear.  I gave a hanger example to make it clear.  What I am trying to calculate is the slip capacity of a bolt with subjected to tension.

RE: Slip Critical Connection

(OP)
Nutte,

Can you tell me where I can find this equation?
Thanks

RE: Slip Critical Connection

Eq. 5.2 in the RCSC Spec. It's in my AISC 13th edition on page 16.2-32.

Certain types of connections usually should be SC - such as bolts in direct tension. I think it was worded directly as such in the 9th edition but the 13th seems to have an overflow of commentary, essentially leaving it up to the EOR whether to pretension or not.

RE: Slip Critical Connection

(OP)
If I understand correctly my slip capacity of the bolt is not effected by external tensile force?
Is that right?

RE: Slip Critical Connection

That is not correct.  Look in the 13th edition page 16.1-110, or 3rd LRFD page 16.1-66, or 9th ASD page 5-74.  Any applied tension will reduce the slip resistance of a slip critical connection.

If the bolt is A325, you're not required to pretension it, although it is probably a good idea to.  However, there is a difference between pretensioning a bolt and a slip critical connection.  Calling for a SC connection requires surface preparation in addition to the pretension.  If you just want a fully torqued bolt, call it out that way.

RE: Slip Critical Connection

(OP)
Thank you all,

RE: Slip Critical Connection

Also check Table 4.1 on page 16.2-23 of the 13th edition

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources