400kV circuit breeaker with capacitor in parallel to the pole

400kV circuit breeaker with capacitor in parallel to the pole

400kV circuit breeaker with capacitor in parallel to the pole

(OP)
Dear all. On site we have a 400kV circuit breaker that connects our step-Up transformer high voltage to the grid substation.
The poles of the circuit breaker have in parallel connection capacitors.
Can you explain why these capacitors are installed?
I guess they are used for precharging of the breaker.
The breaker type is Magrini Galileo 420MhMe-2.

RE: 400kV circuit breeaker with capacitor in parallel to the pole

This is seen in breakers with multiple breaks. If I remember right, the capacitors distribute the restriking  voltage (at the time of breaker opening) across the two arcing gaps) uniformly.

There is a buyers guide for HV circuit breakers available in ABB website. I find it quite informative.

RE: 400kV circuit breeaker with capacitor in parallel to the pole

Parallel capacitors are commonly used in breakers to limit the transient recovery voltage for close in faults. Normally called TRV capacitors.

RE: 400kV circuit breeaker with capacitor in parallel to the pole

Grading capacitors on multi-breaks power circuit-breakers are a necessity to distribute the recovery voltage amoung breaks. Values are in the range of 800 to 2200 pF. Even with them, the first break (on the network side) will see 15-20% more voltage during a three-phase-to-ground fault. This is taken into account during tests.
Single-break breakers may not have a capacitor unless it is recommended by the manufacturer to limit the rate-of-rise of the transient recovery voltages during short-line fauls.

Bahram7
www.Simtech-Intl.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources