Data Center Battery Ground Bus

Data Center Battery Ground Bus

Data Center Battery Ground Bus

(OP)
So a contractor says he measured about 80V AC on the DC battery ground bus (I believe it is 48VDC battery system) for a good size college data center.  I'm not sure where the reference for the measurement was made.  Anyone ever heard of something similar??

RE: Data Center Battery Ground Bus

Sure!  If the DC ground bus is being floated you could easily have ~half the local line voltage appearing on it.  You could test this by hooking an AC trouble light from that ground to an earth ground.  The bulb may partially light if things are really dangerous or it would just drop that measured voltage to zero if it's a low leakage.

NOTE: When 'Data Center' and 'Batterie' are uttered in the same sentence you better be very careful with even tests like that above, as some ground fault system could trip killing your data center.

Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com

RE: Data Center Battery Ground Bus

The last time I saw AC riding on DC like that I found the battery was open circuited and it was comming through the charger.  When I turned off the charger the DC went away and we found a battery connection was corroded open.

RE: Data Center Battery Ground Bus

Really dont like the idea of linking that bulb to ground mate - Most UPS units would pick this up as a ground fault and you could be looking at the unit going to bypass and running the facility at the mercy of the utility....

Hmmmm

First what type of UPS is it ? 48v DC seems a little light for a good sized data centre.

Need to know what UPS you are running, then take it back from there, if you are running a motor gen set type then the thristor driver for the motor may be imposing an ac waveform on the dc link - this would be a duff connection but a good ups would alarm due to this - why was it being checked do you have a problem with it?

RE: Data Center Battery Ground Bus

Last time I saw AC on the DC bus it was in a lineup of medium voltage switchgear with 48VDC floating control power.

Somebody had modified one of the units to be a motor starter.  In the process they re-wired about half of the control panel to run from the local control power transformer.

Typical sloppy practice, they didn't clearly differentiate between the "return" side of the DC ladder logic diagram and the "neutral" side of the AC ladder logic diagram.  They were tied together somewhere in the rat's nest and that made the control power bus for the entire lineup hot.

The "neutral" AC leg was actually one side of a 240V secondary with a grounded center tap.

RE: Data Center Battery Ground Bus

Shows just why its better to have one side of your control circuit grounded, also the dc should always be grounded aswell. Hate floating systems especially in computer rooms.

Rugged

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources