Hi Group

I was recently searching for info on Suction Lift pumping aswell as getting good advice from engtips clown

One bit of Info I found was regarding the suction line and I cant find it again.

I would like to know the recommended min distance of straight pipe at a pump suction before there in an elbow?

Is this the same for all pumps, overhung, double suction, etc?

TIA



-
Milkboy

RE: Elbows and Suction

Recommended min distance is usually 5-10 pipe diameters to stabilize the flow pattern going into the impeller.  It does vary from pump to pump, though, since some are more sensitive to prerotation or un-symmetrical loading than others.

One example would be a double-suction pump that has a vertical vane in the suction nozzle to split the flow between the two impeller eyes.  If there's an elbow in the vertical direction (the most likely in the case of a suction lift scenario), you can actually put it right against the pump nozzle in some cases.  If the elbow is in the horizontal direction, 10 diameters might not even be enough to prevent an uneven 'split' of the flow.

If space is an issue, however, you can get straightening vanes and prerotation vanes that will correct the hydraulics if you can't keep the elbow (or valve, or even a reducer if it's a large enough size change) away from the suction nozzle.

RE: Elbows and Suction

In reality im sure you can get away with 5 diameters, but from a design point of view, pump manufacturers much prefer to have 10 diameters - it is always good, if installation allows, to go nearer this figure in case you do get problems

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources