What is a typical time (or range of times) for a double acting pneumatically controlled plug valve?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Typical time duration from closed to open?
|
RE: Typical time duration from closed to open?
RE: Typical time duration from closed to open?
BigInch
-born in the trenches.
http://virtualpipeline.spaces.msn.com
RE: Typical time duration from closed to open?
Anywhere between 1-2 seconds per inch of pipe diameter works pretty well for two reasons:
1) generally slow enough to prevent water hammer in system
2) can usually be supplied with reasonably sized control circuits and solenoids.
Andy
RE: Typical time duration from closed to open?
-actual torque -> selection of actuator size
-air pressure
-airline pipe diameter and length
-solenoid valve diameter (capacity, Kv)
-throttle valves on solenoid outlets/inlets (if allowed by construction of solenoid valve)
-throttle valves on actuator
-actuator air inlet and outlet diameter and inside construction (length and diameter of inside air tubing)
-actuator size, type and producer
Both short operating time (for instance emergency shutdown) and prolonged (as long as practically limited by equipment) can be 'engineered' by above.
Time limits for control circuits automatically acting on signals from air actuators limit switches therefore either to be given 'ample time' ot to be tested at site if critical for next step.
RE: Typical time duration from closed to open?
RE: Typical time duration from closed to open?
I prefer to select a tubing size that causes some restriction if needed to slow the opening or closing time. More often, a quick exhaust is required to accellerate the closing time for large valves.
The MMS requires offshore shutdown valves to close within 45-seconds. This is difficult with a 36 NPS or larger valve in high pressure gas service. BTW, the valve torque is greater thus closing speed slower when closing against 1200 psig gas in comparison to ambient pressure air.