(OP)
What is the code reference for the 2000cfm requirement of one duct detector and 15000cfm for 2.

RE: Code reference

nfpa 90a 2002 edition


6.4* Smoke Detection for Automatic Control.
6.4.1 Testing. All automatic shutdown devices shall be tested at least annually.
6.4.2* Location.
6.4.2.1  Smoke detectors listed for use in air distribution systems shall be located as follows:  
(1)     Downstream of the air filters and ahead of any branch connections in air supply systems having a capacity greater than 944 L/sec (2000 ft3/min)
(2)     At each story prior to the connection to a common return and prior to any recirculation or fresh air inlet connection in air return systems having a capacity greater than 7080 L/sec (15,000 ft3/min) and serving more than one story

RE: Code reference

2006 International Mechanical Code section 606.2.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources