What is the code reference for the 2000cfm requirement of one duct detector and 15000cfm for 2.
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Code reference
6.4* Smoke Detection for Automatic Control.
6.4.1 Testing. All automatic shutdown devices shall be tested at least annually.
6.4.2* Location.
6.4.2.1 Smoke detectors listed for use in air distribution systems shall be located as follows:
(1) Downstream of the air filters and ahead of any branch connections in air supply systems having a capacity greater than 944 L/sec (2000 ft3/min)
(2) At each story prior to the connection to a common return and prior to any recirculation or fresh air inlet connection in air return systems having a capacity greater than 7080 L/sec (15,000 ft3/min) and serving more than one story
RE: Code reference