BTU from Exhaust stack

BTU from Exhaust stack

BTU from Exhaust stack

(OP)
I need to measure the amount of BTU's taken out of an exhaust stack by a piece of heat reclaim equipment. I need to do it on the exhaust side; the reclaim side has no way of accessing the exchange media.

I have provisions for peto tube type flow meter and temp in and out. Can some make any recommendations on some thing else.

RE: BTU from Exhaust stack

In and out temperatures are a must but pitot tube measurements should be avoided unless there is no other way of evaluating the gas flow.

You also need the flue gas composition to determine the heat transfer.

RE: BTU from Exhaust stack


There is a graph of enthalpy vs temperature (Rosin-Fehling) for all hydrocarbon fuels with curves for different excess air %. Below 500 Celsius the % excess air, has little influence. Thus, by measuring the temperature, the enthalpy of the flue gases is directly determined.

RE: BTU from Exhaust stack

Provided that you know the composition and flow rate of your fuel, you can determine the exhaust flow with an oxygen sensor in the exhaust gas stack. The oxygen sensor basically tells you how much excess air above stoichiomentric conditions you have (neglecting CO and NOx is usually a reasonable assumption for this calculation). This method will also give you the exhaust gas composition. You can work out the enthalpies of each constituent of the exhaust gas and then sum them together in an appropriate manner. The NIST website is useful if you need enthalpy correlations for various gases.

Tim

RE: BTU from Exhaust stack


From reading the above-mentioned R-F graph with my old eyes, the following values of kcal per cubic meter of flue gases at normal conditions (0 Celsius and 1 atm) the combustion carried out with 10-30% xs air, would be

Celsius     Kcal/normal m3

  500              ~180
1000              ~370

Use linear interpolations for intermediate temperatures.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources