checker plate floor loading
Existing 1/4" thick steel checker plate floor is under scrutiny. I'm having difficulty finding a method to determine the maximum allowable concentrated load. A typical plate is rectangular and simply supported on four sides, is removable so not fastened to supports. The load is gravitational so is perpendicular to the plane of the plate. The plates vary in size but an example would be 3 feet by 4 feet. Any thoughts?
RE: checker plate floor loading
Personally, I'd use the "Floor Plate Bending Capacity" tables in the Steel manual, and calculate the equivalent point load from the moment the uniform load would create.
Page 2-145 in the 9th Ed.
Pages 3-154 & 155 in the 13th Ed.
Hope it helps
a=4 b =3. b/a = 1.33 Beta = 0.74 Alpha = 0.0093
Max def = alpha x W x b x b / ( E x t x t x t)
Max stress = (3W /(2 x pi x t x t)) x ((1 + poison ratio) x
ln(2b/pi x r'o) + Beta))
r'o = sqrt (1.6 ro x ro + t x t).
ro = radius of load contact
My 5th Edition Table 25 shows:
alpha=.1478 at a/b=1.2
alpha=.1621 at a/b=1.4
If I remember correctly, don't the building codes define what a "concentrated load" is? It's not a point load, it's something like 2' square (ie, space a person occupies) and that will make a sizable difference in your case. And that would put you closer to formula 1c rather than 1b in Roark's book.
prex
http://www.xcalcs.com : Online tools for structural design
http://www.megamag.it : Magnetic brakes for fun rides
http://www.levitans.com : Air bearing pads