Y-Delta starters in elevators

Y-Delta starters in elevators

Y-Delta starters in elevators

(OP)
OK, pardon my ignorance, but I just cam across a curiosity that has me baffled. Open transition Y-Delta starters that use only 2 contactors! I don't yet know how they are wired because I have seen them only on a bench, but everyone assures me that they are not 2 out of the usual 3 contactors, they are using only the 2. They are mechanically interlocked so that only one can be closed at a time and one of them has a shorting bar across the top. As I said, I don't yet know the wiring configuration, but for the life of me, I cannot figure out how they are able to do anything useful! Has anyone else ever come across this? Apparently, it is very common in the elevator world.

RE: Y-Delta starters in elevators

How many contact per contactor?  Two six-pole contactors would be an easy solution.  Two three-pole contactors might be a bit more of a stretch.

RE: Y-Delta starters in elevators

How about one end of the windings permanently connected to the incoming phases, and the other end of the windings going to two contactors, one to a star point and the other to the incoming phases.

Means there permanently three phase on one end of the windings, but you can still start and stop the motors OK. - saves the cost of one contactor.

Best regards,

Mark Empson
http://www.lmphotonics.com

RE: Y-Delta starters in elevators

Many years ago, I saw a star/delta starter with only two contactors. The star contactor had normally closed, fully rated contacts on the top with three normally open main contacts underneath. Is this the beast?

RE: Y-Delta starters in elevators

(OP)
They are 3 pole, and all of the contacts are normally open.

Marke, that may be it!

RE: Y-Delta starters in elevators

(OP)
For anyone interested or for future reference for searchers, Marke was correct. T1,2,3 leads to the motor are permanently connected to the line, the other 3 leads, T4,5,6,  are connected to a common point between the Star and Delta contactors.

RE: Y-Delta starters in elevators

You just can't assume anything can you!!
Classic case of not doing the obvious and to bad about the safety.

Best regards,

Mark Empson
http://www.lmphotonics.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources