Building Service - Equipment Bonding Jumper

Building Service - Equipment Bonding Jumper

Building Service - Equipment Bonding Jumper

(OP)
If a 12.47kV/480-277V transformer serves a building via underground PVC conduits encased in ductbank, does an equipment bonding jumper need to be routed with the phase conductors from the service disconnect back to the transformer?  This assumes the grounding electrode connection is made at the service disconnect.  It appears the 2005 handbook shows that to be the case for a separately derived system, but other illustrations in section 230-services only show the grounded conductor (neutral) routed back to the transformer.  Thanks for any insight to clear up my confusion or misinterpretation.

RE: Building Service - Equipment Bonding Jumper

If you look at NEC 250-30(a)(1)&(2), you will see that the location of the Main Bonding Jumper and the Grounding Electrode conductor should be as close as possible.  Every building is to have it's own Grunding Electrode, so in the Service Entrance Conductors you do not have an equipment grounding conductor.  At your main you will bond the grounded conductor, (neutral) to the Grounding Electrode and establish your building ground.

RE: Building Service - Equipment Bonding Jumper

I always thought that EC&M magazine went over bonding and grounding examples and explanations of NEC to the Nth degree.  Giving plenty of explanations for every type of installation.

Look here
http://ecmweb.com/

RE: Building Service - Equipment Bonding Jumper

(OP)
Thanks for the quick responses!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources