4.8 kV System

4.8 kV System

4.8 kV System

(OP)
I have encountered the 4.8 kV, 60 Hz system for the first time and I cannot see an overall advantage to it compared to a 4.16 kV system. Circuit breakers come in maximum voltages of 4.76 and 8.25 kV, so the later is needed. Since there is a 4.8 kV generator, it is not inconceivable that it could operate slightly higher sometime. It begins to look like switchgear and wiring must be at 8.25 kV, even though the nominal system voltage is below 5 kV. Does anyone have previous experience with this voltage?

RE: 4.8 kV System

Minor aside: ANSI C84.1-1995 […Voltage Ratings, 60 Hertz] lists 4800V as one of a number of standard ratings for 3-wire medium-voltage service, but not as a ‘preferred’ voltage.  

It is listed in the category of, “…in substantial use in existing systems,” with the comment, “Economic considerations will require that these voltages continue in use and in some cases may require that their use be extended; however, these voltages generally should not be utilized in new systems or in new voltage levels in existing systems.”

Oddly, acceptable voltage limits are: 5080 [>5kV] — 4160 [a preferred nominal voltage itself.]

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources