Generator starting of autotransformer start 1500 HP motor
We're unable to start a 1500hp, 4000 volt motor operating a centrifugal pump under generator power. Pump starts against closed valve that slowly opens in 3 minutes. But we don't get there. Gen manuf.-set CB trips on undervoltage. Generator manufacturer assures us that the gen-set is sized correctly, 1750 KW. Very little other loads. Starter is autotransformer type with taps at 65%. Starter has power factor correction capacitors. Generator voltage before adding load is 4160. New installation, generator manufacture will be out to take a look next week.
Any ideas?
Any ideas?
RE: Generator starting of autotransformer start 1500 HP motor
You can try the 50% tap - since this is a centrifugal pump it can probably accelerate on the lower torque. But the generator is really its own reduced voltage starter in this case - have you tried measuring the actual voltage on either side of the starter during starting?
Does the generator have a voltage boost or voltage support option on the voltage regulator?
You also need to question the setting of the generator undervoltage relay. What it is set at, and why? Undervoltage doesn't really bother the generator too much - if your other loads can tolerate the voltage dip, you may be able to lengthen the time delay on the UV relay.
Lose the undervoltage trip.
Connect the motor to the generator.
Start the generator and ramp the voltage up with the speed. There are a number of ways to do this, both with and without the AVR.
You may use one excitation system for starting and then switch to the AVR.
You may use one or more CTs with resistors across them to develop a load dependent voltage that may be used to fool the AVR into reducing the excitation during starting.
respectfully
Keith Cress
How big is the alternator? The alternator at least should be sized for twice the HP rating.
waross's approach would be like last resort, its far too facny for a new installation. At that point adding a generator in parallel would be more attractive or replace the unit with a bigger one.
There must be an great story behind that technique.....
Did it happen in Alaska?
There are two major components to consider when starting a motor on a gen set.
The engine produces KW and the alternator produces Amps or KVA.
If the engine is too small, the frequency will drop, and if the Alternator is too small, the volts will drop.
Both the engine and the alternator, have an overload capacity and the ability of each to start a motor, is dependant on the overload capacities.
At this stage, it sounds as though you are having a problem with voltage drop, rather than frequency droop, so lets concentrate on this in the short term.
There will be an overload in current during start and the minimum current required is a function of the load torque and the motor starting efficiency. You are already starting against a closed valve, so that minimizes the starting torque requirement.
Using an auto transformer starter can reduce the start current provided that it is set up correctly. In many cases that I see, the motor effectively goes DOL because the transformer steps to full voltage at part speed.
I expect that you are going to need at least the 65% tap to get the pump to full speed, and in many cases, the 80% tap is required to get the motor from 60% speed to full speed. i.e. on the 65% tap, the motor runs out of torque at around 60% speed. This is very much a function of the motor starting characteristics and the load torque.
The first question that I would ask is: Is the trip occuring at the same time as the transformer starter switches to full voltage? Try extending the changeover time ans see if the generator runs for longer.
If the generator is tripping while the starter is on the 65% tap, then you have an excitation problem which is limiting the overload characteristics of the alternator. - This may not be a fault, rather a weakness in the system.
If the alternator is self excited, then the chances are that it will have a short term overload capacity of around 120 - 130%. This is very common on lower cost generator sets. If the alternator has external excitation from a PM generator, then it should be able to supply a short term overload in the order of 300% current.
For this type of application, I always specify a three phase averaging AVR and a PM Generator excitation system. These can usually be added if required.
Self excited systems will commonly require an alternator rated at 250 - 300% of the motor rating to start, PMG excited systems commonly require alternators rated at 120 - 150% to start a pump.
see http://www.lmphotonics.com/genset.htm
Best regards,
Mark Empson
Keith Cress
As you will not from various other threads related to this topic in this forum, what gets "warm" the most during these aborted starts is the rotor and it can take a long time for that heat to make it out to the housing of the motor. Never rely on the housing temperature of motor to decide that it is cool enough to try to start it again. As long as the prime mover continues to run the generator should be getting plenty of cooling air, but watch that motor rotor.
A VFD was suggested. Rather than using a VFD to ramp up the frequency and voltage, it would be very simple and cheap to use the generator to do the same thing.
With further thought, after disabling the undervoltage trip, if the motor is connected directly to the generator and the engine then started, the underfrequency roll-off feature of the Automatic Voltage Regulator will do a pretty good job of ramping the voltage up as the frequency increases. It should bring the motor up to speed efficiently and with a lot of the advantages of a VFD start.
If this technique is used, I would go direct online and not use the autotransformer starter.
Use a UPS to energise the main contactor in the starter.
A variation of this technique is used to energise Generator Step-up Units. Why not motors?
respectfully
Your approach has merit. The only difference in a step up tranformer and starting a motor is the starting torque requirement and some real power. Real power is not a problem in this case, the reactive power and the torque requirement is. At very low voltage motor may just stall or draw excessive current.
I believe by defeating UV protection during the start should help a great deal. I would also try at higher voltage than lower, if necessary. All other cautions about motor heating up mentined above are also valid.
There may be a fair amount of protection that would have to be circumvented. I agree that that UV relay is probably not necessary unless they plan on operating in parallel with utility at some point.
Got a +500HP motor lying around? Hook it up in a manner where you start it with the generator. Once it's running start the large motor. It will return energy to the system in parallel with the generator. It may be enough to do the trick. You could disconnect it once it has returned all the energy it's going to, based on the current direction to it. For more stored energy add a flywheel to it.
Another alternative would be a pony motor to get the 1500 up to some speed that the generator can then support a start of.
Keith Cress
If so, and that motor protection relay is not tripping, the generator breaker has no business tripping on UV. Delete/defeat that.
Re the reduced speed starting technique:
The Electric Machinery Mfd. Company used to publish an information magazine called the "Synchronizer" (E-M Co. invented, and produced the original field frequency relay.)
In issue #200-SYN-59 they discuss starting large motors on generators.
The techniques discussed:
Shunt capacitors to supply the KVA demand.
About 800% of the capacity used for normal power factor correction will provide about 50% of the starting KVAs. The capacitors must be cut out in steps as the motor is accelerated or serious overvoltages will result with the generator.
Initial voltage boost.
A resistor is inserted into the voltage measuring circuit to fool the AVR into over-exciting and driving the voltage higher. The motor is connected as the voltage is increasing. The timing would be less than a second.
Simultaneous start.
The motor is connected to the generator. The generator field is energised and the generator started and brought up to speed. Applicable to Hydro and steam turbines.
Sub frequency start.
The prime mover is started and run at an idle and the motor is connected. The field is energised and the motor is accelerated up to speed.
Applicable to diesel engine sets.
Note; Under Frequency Roll Off equiped Automatic Voltage Regulators were not common when this was written.
Voltage is dependant on speed as well as field strength. With full excitation on a set running at 50% speed, the set will produce 50% voltage. As a result we have a fairly constant volts-per-hertz ratio supplied to the motor similar to a VFD drive.
Old style AVRs lacking UFRO would try to maintain full voltage at reduced speed. The normal result was the AVR regulator and failing if the prime mover was run at much below rated speed. The old regulators had a manual switch and were not normally turned on until the prime mover was up to speed.
What I would expect to happen with your set (after you get rid of the undervoltage trip) is that the starting energy demanded by the motor will drag the frequency down. This will result in a reduced demand for starting energy. At some frequency/speed below 60Hz the energy output of the diesel will meet the reducing energy demand of the starting motor and the speed/frequency will stabilize. The UFRO feature of the AVR will have reduced the voltage proportionately. The motor magnetic circuit will not saturate because the volts-per-hertz ratio will have been almost constant. The starting current will be less than across the line because of the reduced voltage. Both the motor and the genset will accelerate together until the frequency is up to 60Hz. The starting cycle will probably be a little longer than across the line utility starting but it should still be quite friendlly towards both the motor and the generator
I understand that you have already installed the equipment. Equipment changes at this time will be expensive and emarrasing.
The first step, lose the undervoltage trip.
Then do a series of starts and observe the action. Start with the autotransformer starter. Start without the autotransformer.
If you want less voltage drop, try adding a resistor and using some voltage boost.
You may consider taking your notes to a quiet place and spending some time adding the information to your documentation beteew starts. It is a good way to force the more impatient team members to allow adequate cooldown time between starts. You may alsow want to let the motor run for 10 or 20 minutes before stopping it. The rotor cools quicker when it is turning, and a 20 minute run time limits you to 3 starts per hour.
dpc;
Never worked in Alaska. I did have some fun with a couple of small generators in the Yukon teritory just east of Alaska. The highlight of that adventure was a 10 day canoeing and hunting trip down the Big Salmon river and part of the Yukon river. My partner got a nice moose. It almost sank the canoe. One trip travelling back south I had a few adventures on the road where jraef ran out of gas. I think he mentioned it in Pat's Pub.
A lot more fun than the generators.
respectfully
Now where's those cool plots??
Keith Cress
Thank you for the feedback. I am glad all worked out for you. Hopefully you have all protective settings reviewed by some competent professional.