Pretension Load for Guy Wire Supported Flare Stack
Pretension Load for Guy Wire Supported Flare Stack
(OP)
Any guidelines/formulas/references how to calculate pretension load for guy wire supported flare stack. Is it percentage of the cable breaking strength? Thank you very much.






RE: Pretension Load for Guy Wire Supported Flare Stack
Dik
RE: Pretension Load for Guy Wire Supported Flare Stack
Towers And Supporting Structures' states "Initial tension in the guys, for design purposes, is normally 10 percent of the published breaking strength of the strand with upper and lower limits of 15 and 8 percent respectively. Values of initial tension beyond these limits may be used provided consideration has been given to the sensitivity of the structure to variations in initial tension and, if necessary, to dynamic behavior (see note below). Consideration shall be given to the site ambient temperature range. In the absence of site specific data, the initial tensions shall be based upon an ambient temperature of 60°F." as found at http://www.floridatowers.com/tia222f.htm
RE: Pretension Load for Guy Wire Supported Flare Stack
Dik
RE: Pretension Load for Guy Wire Supported Flare Stack
We use Galvanized Bridge Strand for the guy ropes on our Stacks which are pre-stretched by the manufacture to eliminate most of the construction stretch.
The initial pretension that we use is nominally 4.5% of the breaking strength with a minimum of 2.5% in the most unfavorable cold stack/hot ambient combination.
If you have a cold stack condition (stack shrinkage) and a hot ambient temperature (rope growth), the ropes will start to go slack and lose some of the pre-tension. In this condition we want to have a pre-tension of at least 2.5% of the breaking strength.