G.C. wants to install a 3x nailer on the top of w10x steel beam at the field, the provisions were not to drill in the moment frame top flange or web, G.C. suggests to install a shop weld steel plate 1/4" x 3 1/2" x 8" @16" o.c. at the side of top flange and use lag screws for nailer attachment as a replacement for welded studs at top flange.
Any help would be greatly appreciated.
Any help would be greatly appreciated.





RE: Wood nailer on steel beam
Dik
RE: Wood nailer on steel beam
RE: Wood nailer on steel beam
Dik
RE: Wood nailer on steel beam
RE: Wood nailer on steel beam
Lining up holes for the nailer in the field is not difficult. The holes should be field drilled.
Suggestions:
1. Contractor replaces the bent threaded studs. Handling of the material is a contractor's responsibility. Definitely try to assist the contractor with a solution.
2. Powder actuated fasteners - can be okay if the loads are not big requiring a lot of fasteners. I believe that there is a legacy report for these. I do not know if the city of LA is included.
3. Weld leg of angle to underside of top flange of beam. Powder actuated fasteners into the side of the nailer. Again, loads need to be considered for feasability. Consider staggering the angles on each side of beam.