NFPA 72- Fire Alarm question...
NFPA 72- Fire Alarm question...
(OP)
Does anyone know any further wording in NFPA that talks about any fire protection equipment, device, system, ect...that if installed (no matter when) it must be 100% operational or removed if not needed or required?
The only thing I am coming up with is NFPA 72, paragraph 4.3.1.
Does anyone have a more information pleasze ?
The only thing I am coming up with is NFPA 72, paragraph 4.3.1.
Does anyone have a more information pleasze ?
Joe G. Willett
Jacksonville, AR





RE: NFPA 72- Fire Alarm question...
RE: NFPA 72- Fire Alarm question...
Joe G. Willett
Jacksonville, AR
RE: NFPA 72- Fire Alarm question...
RE: NFPA 72- Fire Alarm question...
I don't have it handy, but the National Fire Code (partner to BOCA buidling code) has something along the lines of:
You can't leave an abandoned fire sprinkler system in place. I am a sprinkler guy so I am not sure about fire alarms but would think it was similar.
I have been told that the theory was you don't want some one supplying new sprinklers from the abandoned pipe and thinking it is connected to the water supply. You would drain the system before working on it, so both would be dry when you go to make changes. Then, you fill it back up and leave. However, the changes you just did would not be connected to a water supply.
This sounds really confusing as I write it, so I hope you get the idea. I would assume the IFC has something similar. Again, that is Stookey's area of expertise, so hopefully he will chime in on this.
RE: NFPA 72- Fire Alarm question...
2006 IFC section 107.5 states that you cannot render a fire protection system inoperable. The intent is if one provides a fire protection system, even if it is no longer required, it cannot be rendered inoperable. The intent is that a fire protection system should not cause the building occupants or firefighters to believe that a building is protected when in fact, it is not.
IFC 901.6 further requires that nonrequired fire protection systems shall be inspected, tested and maintained. If the owner does not satisfy this, it must be removed and the IFC grants the code official to require the removal of the nonrequired system.
If the system is no longer required you have two options:
-- Maintain it in accordance with the construction standard and mainetenace standards adopted at the time of its installation - or -
-- Yank it out of the building.
RE: NFPA 72- Fire Alarm question...
That is exaclty how I see it too, I just could not find the wording in NFPA; I will get a hard copy of the IFC paragraphs.
Thank you so much. Now I can have a good weekend!!!!
:)
Joe G. Willett
Jacksonville, AR
RE: NFPA 72- Fire Alarm question...
I thought the federalies adopted a building/ fire code for bases or had to go by the local code adopted by the city.
You will not find anything that says to remove it, but fire code says maintain it.
I know bases use a standard jsut do not know what it is any more.
have you called GSA
ht
http
h
RE: NFPA 72- Fire Alarm question...
I am not sure if this will apply, but try looking for info here regarding the UFC (Unified Facilities Criteria) codes.
h
The Fire Protection Design is under the following section UFC 3-600-01
Hope I could help
BDK
RE: NFPA 72- Fire Alarm question...
A storage facility, used for hazardous waste accumalation not limited to battery storage, water reactive corrosives, flammable liquids/solids, ect.. The facility is 1600 sq ft. Built in late 80s, built with suppression, detection, and explosive proof electrical. Inside the facility are 3 rooms, divided by 2 hour walls, may even be 4 hour, im not sure, these rooms all have exit doors that lead directly outside. Each of these three rooms also have overhead rolling doors. In the event of a fire alarm, the rooling doors close automaticvally and they have heat links too.
Currently, the doors will not close or operate when the fire alarm goes off; my question is, IAW NFPA or any other code, must the overhead rolling doors operate today with the fire alarm as they were desighned, installed and built to do originally?
Joe G. Willett
Jacksonville, AR
RE: NFPA 72- Fire Alarm question...
The normal answer is if something was installed it has to be maintained and operational.
I do not think there is a code requirement unless once again you are doing a protected opeing to require the door to drop from a fire alarm. I believe most codes now a days for overhead doors only require the fusible link, which I do not agree with.
Do the doors even close if the link is cut or is it just the electronics fromm the fire alarm that is not dropping the door????
RE: NFPA 72- Fire Alarm question...
The overhead rolling doors, will drop if the fire link is fused, and they will also drop down electrinically if the fire is activated or activates.
Joe G. Willett
Jacksonville, AR
RE: NFPA 72- Fire Alarm question...
Should have asked if they carry a fire rating???
Same answer though if it is there normally has to be maintained.
In the international code for rolling shutters it says close using approved automatic closing devices.
in the uniform code it says fusible link or smoke detector
RE: NFPA 72- Fire Alarm question...