Question!:
I am looking at running a water line to a site that contains two buildings which are split into eight units. Each unit requires a seprate water and sewer service. So, there is a 6" DIP "main" line coming into the site, with 2" (for now) water service lines into each unit.
The question arose that IF they decide to sprinkle one of the buildings, the service sizes would change from 2" to something larger. THEN, would a 6" main line be able to support the increased fire flow?
I learned from the City that the static pressure of the main, just outside the property, is 60 psi. The total length of the 6" line is about 300'.
Any opinions/advice on this would be much appreciated!
I am looking at running a water line to a site that contains two buildings which are split into eight units. Each unit requires a seprate water and sewer service. So, there is a 6" DIP "main" line coming into the site, with 2" (for now) water service lines into each unit.
The question arose that IF they decide to sprinkle one of the buildings, the service sizes would change from 2" to something larger. THEN, would a 6" main line be able to support the increased fire flow?
I learned from the City that the static pressure of the main, just outside the property, is 60 psi. The total length of the 6" line is about 300'.
Any opinions/advice on this would be much appreciated!





RE: Fire Pressure
If you are on a relatively flat site, 60 psi at the property line should be adequate. You will probably figure in around 100 gpm domestic allowance in the fire line to be added to the sprinkler system. Therefore, you are only going to need about 200 gpm (100 gpm domestic allowance + 80 gpm for sprinklers + 20 gpm for over-discharge). The greatest pressure loss is when you size the incoming fire line supply to the building too small. I often see engineers trying to bring in a 1.25" or smaller line for the fire demand. If you flow 80 gpm through that, you eat up a lot of pressure. Do it with a 2" line and you are likely OK.
If you are required to provide protection per NFPA 13, then you would want a minimum 4" line to come into the building. However, the 6" site main should still be adequate.
Good luck!!
RE: Fire Pressure
Thanks again!
RE: Fire Pressure