Gentlemen
we use a plasma cutting equipment that may be seen from the supply side as a three-phase transfomer. For safety reasons it might be switched on and off quite frequently, say every ten minutes in worst cases.
The primary voltage is 400 V, the size of transformer is 50 kVA.
Is there a proven and cost-effective solution to limit the inrush current?
Will a set of three resistors by-passed after a short time do the job?
Not a real problem, I am trying to improve and reduce potential causes of trouble since we have a lot of delicate equipment around.
thanks for your time

RE: small three phase transformers inrush current

Hi there!
doesn't plasma welders work with very high inrush currents? I dont see how by avoiding the inrush current, you will be able to run your welder. This is the way I understand your commnent, if you can be more specific please state so...
Regards

RE: small three phase transformers inrush current

well...by plasma welder I also meant plasma cutting equip. as you stated.
Regards

RE: small three phase transformers inrush current

I3city;  fab will suffer regular large inrushes switching on his 50kva transformer that has nothing to do with cutting and will, in fact, be much larger.  It has to do with when the transformer was turned off in the power cycle and when it is turned back on.

fab; Certainly a switched in/out resistance will do the trick.  Might be interesting too to just turn the unit on and off at just the correct point in the power cycle.  You'd only need to monitor one phase obviously.  I wonder if anyone has tried that..

Otherwise you'd just run an "ON DELAY" relay to cut in a shorting contactor around your resistance 1 second after the ON switch is turned on.

Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com

RE: small three phase transformers inrush current

I wonder if a capacitor contactor with the pre-charge block would work in this application. When they close they first connect through resistors or resistor wire then connect the main contacts. I have no idea how well they work but they are available.

RE: small three phase transformers inrush current

(OP)
thanks to everybody for your prompt replies and advice

RE: small three phase transformers inrush current

itsmoked,....thanks for clarifying:
  "It has to do with when the transformer was turned off in the power cycle and when it is turned back on"
I kept thinking of just the plasma welder not the whole picture (engineering basic mistake, jajaja!)
Regards

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources