Dear fellows:
Could someone please advice me on the correct method for de-scaling a water cooled condenser? If it is really done with a solution of phosporic acid, what are the mix proportions? Also, what kind of pump should I use to handle this solution?
Thank you!!
Could someone please advice me on the correct method for de-scaling a water cooled condenser? If it is really done with a solution of phosporic acid, what are the mix proportions? Also, what kind of pump should I use to handle this solution?
Thank you!!





RE: Water cooled condenser scale removal
In most cases, inhibited hydrochloric acid works well for removing carbonates. If silicates are a problem, add a little hydrofluoric, but beware of the increased danger to humans & material. Usually, best to use commercial descaling products, as already contain the right amount of inhibitor.
RE: Water cooled condenser scale removal
I would talk to a water treatment contractor/supplier before rushing in. Running the solution too hot can damage/destroy copper tubes. Goodluck
I'm not a real engineer, but I play one on T.V.
A.J. Gest, York Int./JCI
RE: Water cooled condenser scale removal
RE: Water cooled condenser scale removal
I hope this is of some help.