Looking for way to correct problem in exsiting switch gear that utilizes 5/16" all thread to hold C channel barrier for buss spacing, from heating... temp. showing 54.6 C on all threads, buss running at ambient room temp.
Am considering covering all tread with tublar barrier board.
Thanks for any help
Am considering covering all tread with tublar barrier board.
Thanks for any help






RE: EMF between phase buss
If you can surround all three phases you won't see the heating. Or somewhere break the hanger loops with non-metal sections.