EMF between phase buss

EMF between phase buss

EMF between phase buss

(OP)
Looking for way to correct problem in exsiting switch gear that utilizes 5/16" all thread to hold C channel barrier for buss spacing, from heating... temp. showing 54.6 C  on all threads, buss running at ambient room temp.

Am considering covering all tread with tublar barrier board.


Thanks  for any help

RE: EMF between phase buss

That will likely not work.
If you can surround all three phases you won't see the heating. Or somewhere break the hanger loops with non-metal sections.

Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources