Is the step & touch potential and related earthing also applicable for an indoor buil subsation ?

thanks

RE: step & touch potential

Basically, yes.  The environment is different, but the risks are the same.

RE: step & touch potential

Yes, the step & touch potential and related earthing apply for indoor substations.

The most usual differences are:
a) Indoor substations are smaller in area than the outdoor one creating additional challenge to achieve the desire grid resistance.

b)That the allowable step and touch potential for outdoor substation is ussually larger than indoor substation.  

For instance, indoor substations usually have concrete slab floor with low resistivity (50 to 90 Ohm.m) while outdoor substation usually have crushed rock with wet resistivity of 2000 to 3000 Ohm.m.

Shoes, paint coating or insulated mat may be considered in the analysis for improve the allowable step and touch potentials in indoor substations.

RE: step & touch potential

The concrete slab will have will have steel rebar which will make it almost an equipotential surface.  Unless the switchgear is GIS with very high fault currents possible through the enclosure, I don't think that you need to consider touch and step potentials inside the building.  You should determine what the touch potentials are to the building itself for someone standing outside.

RE: step & touch potential

I'd put a copper mesh (6" x 6" or 12" x 12" grid) into the concrete floor slab, extending out 8 to 10 feet from the gear.  That mesh should be bonded to the ground bus in the gear as well as the floor rebar.  The rebar ties may or may not have a good electrical connection.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources