Explosion Proof - Electric Radiant Heat Panel

Explosion Proof - Electric Radiant Heat Panel

Explosion Proof - Electric Radiant Heat Panel

(OP)
I am in need of explosion proof radiant heat panels for a class 1 div 1 facility.  I checked with Chromalox and had no luck.  Would anybody be able to suggest a manufacturer?  

Thanks in advance.

RE: Explosion Proof - Electric Radiant Heat Panel

Can't you use explosion proof unit heaters instead. They are readily available.

RE: Explosion Proof - Electric Radiant Heat Panel

check Indeeco, they are the name is explosion prooof

RE: Explosion Proof - Electric Radiant Heat Panel

(OP)
I was going to go with unit heaters (as I did in other rooms of the building), but this equipment is for the screen room of a water treatment plant.  The room is mostly unoccupied, but the wastewater engineers were concerned about pipes freezing, etc.  The room has a 5,000 cfm exhaust/air filtering system that is constantly running...so I figured a radiant heater may be the better choice.  

I called Indeeco, and they said they didn't manufacture such equipment.  I'm wondering if I should be asking for "tube" instead of panels.  Does asking for the panels imply the ceiling tile type??

Thanks again for the replies.

RE: Explosion Proof - Electric Radiant Heat Panel

Your choice of system is not right.
For sewage pump station, you need to supply and exhaust air at 12 ACH while maintaining negative pressure with dual flow rates if you have gas and oxygen sensors and the like, see NFPA 820 ventilation chapter.
YOU need an Indeeco explosion proof duct mounted heater upstream of the supply fan.
Why go radiant when what you need is to heat the OA coming in, not the objects in the space.
How come your screen room is occupied? Screen rooms are seldom occupied, stinks like hell in there, one could pass out easily from exposure to excessive H2S if they stayed long periods in such an environment.

Read your NFPA 820 and stick to that, stop messing with your brain about system choice.

RE: Explosion Proof - Electric Radiant Heat Panel

Forgot to mention, use explosion proof electric unit heaters in addition to the duct mounted heater as Lilliput suggested.
You now have your system complete.

RE: Explosion Proof - Electric Radiant Heat Panel

(OP)
Thanks Atlas.  I totally agree with you and the space not being occupied.  I worded it wrong.  What I meant by "mostly" was the occasional worker walking in there for whatever the reason may be.  The room was designed according to NFPA 820 Class I Div I criteria.  The reason I was leaning away from the explosion proof heaters is for the soul reason that it seems like a waste to temper all that incoming air when the space is typically unoccupied.  I'm new to the field, but the two sewage stations that I did visit lacked heating in the screen rooms.  Initially I thought a room like this wasn't heated.  The main concern is was the equipment freezing, therefore I figured it would save energy heating the actual objects in the room and not the incoming air.  Please correct me if my reasoning is wrong.  

Thanks again.      

RE: Explosion Proof - Electric Radiant Heat Panel

If the room is exhausted, it is better to have a makeup air heater to heat outdoor air prior to introducing it into the building. Otherwize the exhaust will pull in infiltration - unheated outdoor air anywhere there is a crack or opening on the building envelope, creating freezing problems.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources