Called to replace a 230 volt 3 phase delta wound motor.
Motor had caught fire, no one could tell me when it had caught fire, (at start or while running) everyone knew nothing...
Sent the motor off for rewind.
While waiting for motor to be returned, tested the starter.
The start starter closed then 11 seconds later the run starter closed.
I have never seen a pert winding starter set that long.
Could this have started the fire?
I am used to 2 seconds delay, not 11 seconds with part winding motors.
What is your opinion on the timing.
Thanks, Joe
Motor had caught fire, no one could tell me when it had caught fire, (at start or while running) everyone knew nothing...
Sent the motor off for rewind.
While waiting for motor to be returned, tested the starter.
The start starter closed then 11 seconds later the run starter closed.
I have never seen a pert winding starter set that long.
Could this have started the fire?
I am used to 2 seconds delay, not 11 seconds with part winding motors.
What is your opinion on the timing.
Thanks, Joe





RE: Part Winding Motor, Starter Timing
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Part Winding Motor, Starter Timing
respectfully
RE: Part Winding Motor, Starter Timing
RE: Part Winding Motor, Starter Timing
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Part Winding Motor, Starter Timing
RE: Part Winding Motor, Starter Timing
The motor is a 230/460 50 hp 3 phase 9 lead motor connected to a part winding starter wired for 230 volts. it is connected to a pump for a water slide.
I suspect two things, 11 seconds timing is way too much and attendants stopping and restarting the motor/pump while their friends were on the slide. (prank)
Thanks again for your opinions.
RE: Part Winding Motor, Starter Timing
Here is the problem with Part Winding (PW) starting;
1) Low starting torque on the start winding (50% of FLT) which is sometimes not even enough to turn the shaft. The real purpose is to just establish the magnetic fields in the stator and rotor at a lower inrush (not necessarily starting current if you understand the difference) in preparation for the remaining windings to act to accelerate the motor. 1-2 seconds in Start is MAXIMUM. Longer settings will NOT reduce the starting current, a common misconception brought about by people not really understanding the concept yet using it to satisfy a utility requirement for Reduced Voltage starting. In actuality, utilities should NOT allow PW starting to be classified as such because it only reduces the voltage drop if the problem is a weak transformer, not a weak supply.
2) The motor heating during Start is extreme compared to any other method of RV starting. You are essentially at locked rotor current for a smaller motor, 50% of the main motor size, but the rotor may not actually be turning so that current stays that high without doing useful work. Again, remember that the intent was never to try to accelerate the motor, just to establish the magnetic fields. Therefore any more than a couple of seconds serves no useful purpose other than to begin to deteriorate the winding insulation.
In addition to someone cooking your winding by setting the transition time beyond 2 seconds, you have the other problem of short cycling. I strongly suggest you install a lock-out timer in your control circuit. This is usually highly recommended by motor manufacturers for PW started motors for the very reasons stated above. A good solid state Overload Relay that includes that feature would be worth the price of avoiding the next rewind.
JRaef.com
"Engineers like to solve problems. If there are no problems handily available, they will create their own problems." Scott Adams
For the best use of Eng-Tips, please click here -> FAQ731-376
RE: Part Winding Motor, Starter Timing
RE: Part Winding Motor, Starter Timing
When I was young and knew so much more than I do now, I knew those connections by heart. I connected two 40 HP blowers by the numbers. After the BANG BANG, (both motors started automatically in sequence) I discovered that those motors did not use NEMA numbering. The numbers were actually 6,7,8, not 7, 8, 9. It blew the internal star points open on both motors.
The good news was that warranty covered the repairs. My employer offered to pay for the damage that I had done, but the shop said that they felt that the motors should have withstood the abuse without those connections opening and so would support a warranty claim. Good people to deal with.
I always double check ther nameplate now.
respectfully
RE: Part Winding Motor, Starter Timing