Dowels only for shear transfer
Folks,
I have a project involving a short plain concrete wall on a plain concrete footing (ease of construction).
The wall and footing will (likely) be cast-in-place using slipform methods.
What is the formula for calculating the shear transfer provided by regularly-spaced dowels at the joint between the two elements (wall and footing) assuming that:
1) no special roughening is performed,
2) no key shape is cast into the top of the footing
The project is being designed in accordance with AASHTO HB-17/2002, if that helps.
It's been a long time since my college structural design courses, so please be nice and furnish a brief explanation of the nomenclature.
Jeff
Jeff
RE: Dowels only for shear transfer
Vn=Avf*fy*(coefficient of friction). Vn is the nominal shear resistance provided by your regularly spaced dowel, Avf is the area of your regularly spaced dowels (in in^2/ft), fy=the yield stress of your Reinforcing bars (60ksi), and I would use the coefficient of friction of 0.6 for concrete place against hardened concrete not intentionally roughened per 11.7.4.3.
Hope this helps.
For the "Strength Design Method", this is covered by formula 8-46 of section 8.16.6.1.1.
Vu < phi x Vn
Vu is defined in 8.1.2 as the Factored shear force
phi is defined as 0.85 in 8.16.1.2.2
Vn is defined by formusl 8-56 in 8.16.6.4.4. as follows
Vn=Avf x fy x mu
Avf is defined in 8.1.2 as the area of shear friction reinforcement
fy is defined in 8.1.2 as the specified yield strenght of reinforcement
mu is defined in 8.16.6.4.4(c) as 0.6 x lambda, for concrete not intentionally roughened
lambda is definded in 8.16.6.4.4 as 1.0 for normal weight concrete
According to 8.16.6.4.5,
Vn < 0.2 x f`c x Acv and Vn < 800 x Acv
where Acv is the area of concrete resisting shear transfer.
Naturally, I will have a structural designer prepare the final design, but I want to verify that my proposal will pass muster in advance.
Basically the wall will be a gravity retaining wall. Since the cheapest way to construct it will be slipforming as described above, I will need to transfer horizontal loads to the separately cast footing. The wall will need to provide lateral resistance in both directions, due to the possibility of traffic impact.
Jeff
I do, in fact, have a copy of the ACI code available.
Jeff
Much appreciated.
Jeff