Does anyone know of any design guides/formulas for the bending moment distribution for a concrete wall panel used as cladding on a single storey portal frame building subjected to lateral wind loads?
The base of the panel is considered to be fully supported (tied into floor slab), and the top 2 corners are fixed to the steel columns via steel plate clips.
The base of the panel is considered to be fully supported (tied into floor slab), and the top 2 corners are fixed to the steel columns via steel plate clips.






RE: 2 way spanning concrete wall panel
RE: 2 way spanning concrete wall panel
You can calculate panels as a slab loaded normally with the distributed wind load and no self weight. Please check whether you can assume simple support on the vertical and top sides since you say you have ties only in the upper corners, not along the entire length of these sides.
Also, are these panels expected to carry loads in their plane besides the self weight (wind/eqrthquake along the longitude of the structure) or you have provided bracing otherwise and use panels just for cladding?
Mike
RE: 2 way spanning concrete wall panel
This is a very bad detail when it comes to behaviour of the panels in fire.
The portal frames will tend to 'soften' in the fire and the rafter portion will sag in the middle forcing the columns to bend inward. Meanwhile the panel will be hotter on the inside than the outside therefore causing the panel to curl outwards. the result is a prying action that can cause sudden and severe outward collapse.
Best to design the panels to span one way only if this is possible.