GROUND FAULT SYSTEM FOR 240-120 DELTA

GROUND FAULT SYSTEM FOR 240-120 DELTA

GROUND FAULT SYSTEM FOR 240-120 DELTA

(OP)
WHAT GROUN FAULT PROTECTION SYSTEM METOD IS RECOMENDED FOR
A SWGR 240-120 V

RE: GROUND FAULT SYSTEM FOR 240-120 DELTA

Normally the neutral of the 120/240 leg is grounded.
A ground fault detection system is not used with a solidly grounded system.
If you use a high resistance ground on the neutral, you must use a ground detector which can accept 120 volts, 120 volts and 208 volts as normal inputs, or monitor the grounding resistor voltage or current.
If the neutral is not used, a delta type ground detector may be used.
The code may require the neutral point to be solidly grounded.
respectfully

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources