I am using ENERCALC to design some tilt walls. ENERCALC lets the engineer select the ACI 318-02 procedure. Under this analysis procedure, you can select a base fixity for the tilt panel. How do you determine the amount of fixity at the base of the panel? The program let's you select a fixity from 0 to 100%. Also, what types of details are usually provided to give fixity at the base of the panel. Thanks.






RE: tilt wall base fixity
RE: tilt wall base fixity
If the panel is simply doweled to footing or slab, it is pinned. If you have to achieve fixity, the way I have seen it done is to provide a deep slot in the footing, which is in turn grouted when the panel is in place. Of course, the footing has to be designed accordingly for the overturning, etc.
RE: tilt wall base fixity
I wouldn't call that 100% fixity, perhaps 50 - 75%?
RE: tilt wall base fixity
Good luck,
YS
B.Eng (Carleton)
Working in New Zealand, thinking of my snow covered home...
RE: tilt wall base fixity
Regards,
YS
B.Eng (Carleton)
Working in New Zealand, thinking of my snow covered home...
RE: tilt wall base fixity
RE: tilt wall base fixity
RE: tilt wall base fixity
My personal opinion and interpretation of this guidance is that going above this level would require specific detailing.