Asynchronous Motor - Decay of motor fault contribution

Asynchronous Motor - Decay of motor fault contribution

Asynchronous Motor - Decay of motor fault contribution

(OP)
IEC60909-0 uses empirical formula to calculate the decay in asynchronous motor fault current contribution at given times after fault inception.
Can anyone provide actual information on the decay of fault current contribution from asynchronous motors ?
The plant in question has 23MW of 6.6kV motors, and 51MW of 440V motors.  The plant has 80MW of local generation at 6.6kV, and a 132kV Utility interconnection.
We wish to use the hi-set pickup of directional relays to provide reactor protection.  The directional relay must be delayed by approx. 40 msec to allow it to determine direction.
How much will the asynchronous motor fault current contribution have decremented 40 msec after fault inception ?

RE: Asynchronous Motor - Decay of motor fault contribution

It is difficult to give any general answer, because the decay of the current depends on several factors, such as the motor type and pre-fault loading, location of the fault, etc. Simulation with ATP, EMTP or similar program would perhaps give the best answer. You might also get some idea of the decay of the current by using a power system analysis program that calculates the currents as a function of time. See http://pp.kpnet.fi/ijl

RE: Asynchronous Motor - Decay of motor fault contribution

The larger the motor, the longer the decay time.  I do know of a refinery that was blacked out because the directional relays  mis-operated due to motor contribution into a fault well out on the utility system - so be conservative.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources