How to transition from PVC Force main to HDPE force main?

How to transition from PVC Force main to HDPE force main?

How to transition from PVC Force main to HDPE force main?

(OP)
I have an 8" force main that is PVC that I need to transition to HDPE in order to do a directional drill for a section. How would I transition this pipe from PVC to HDPE and back? What type of coupling or transition collar?

RE: How to transition from PVC Force main to HDPE force main?

A MJ adapter would work.

I usually spec out a larger HDPE pipe to meet similar internal diameters.  So if I had an 8" pvc line and my HDD was 10" HDPE, my callout would look like this:

STA xx+xx, xxLT/RT, Construct:
(1) 2" Manual ARV
(1) 8" Plug Valve
(1) 8" 11.25-Degree bend
(1) 10" x 8" reducer
(1) 10" MJ HDPE/PVD Adapter

RE: How to transition from PVC Force main to HDPE force main?

(OP)
CivEnvEng98:

What is your 11.25 bend for? Why is the air release valve necessary?

Thanks

RE: How to transition from PVC Force main to HDPE force main?

gt5879c,

The bend is to transition to the bore angle, which is typically 10 to 13 degrees downward at each end.  A fabricated HDPE fitting is much more expensive than a "off the shelf" DIP fitting and probably quicker to procure.  It's your choice.

The arv is to help vent the high points in your line.  The bore creates 2 high points, one at each end.  Some only put one arv on the upstream side, but I always specify 2 for improved maintenance.  I suggest manual ARVs unless the utility specifies the automatic style.

RE: How to transition from PVC Force main to HDPE force main?

molded flange adapter for the HDPE (the molded flange adapter will also need the heavy duty back up ring, red rubber gasket and 8 bolts)
flange to mj adapter (with PVC megalug gland, transition gasket and red rubber gasket and 8 tblots)

would be what I would use to connect PVC to HDPE, also be sure to check for material homogenialites between the flange adapter and pipe

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources