Current Transformer leads/other wires in same conduit

Current Transformer leads/other wires in same conduit

(OP)
I have two conduits to an outdoor switchgear.  One conduit will contain 24 VDC power and control wiring. The other will contain 120 VAC power wiring.  Also, in the switchgear there is a set of 100:5 Current transformers.  I need to bring the leads from those ct's back in one of the two conduits.  Which one?

RE: Current Transformer leads/other wires in same conduit

I would vote for the 24VDC conduit. If you're using the CT for revenue metering, I would recommend running shielded, twisted-pair cable. Otherwise, it shouldn't really matter.

RE: Current Transformer leads/other wires in same conduit

Probably either one will work.  The 24 V dc conduit will be safer for the CT circuit.  I suppose there's a chance that a fault that put 15 or 20 amps through the CT secondary could cause your dc control circuits some heartburn, but I've never known it to be a problem.

RE: Current Transformer leads/other wires in same conduit

Metering connections commonly run CT currents in the same conduit or cable as the 120 volt PT circuits.
I understand the constrictions of using existing conduits, but given the implications of an open circuit on a CT secondary, I would investigate whether it is possible to run another  conduit dedicated to CT and PT wiring.
If not possible, I would go with the 120 volt circuits. I would try to physically arrange the CT wires or cable so that it is unlikely that it would be inadvertently opened under load. Remember that depending on the impedence of the load, a CT secondary may show a very low, supposedly safe voltage under load, but if the circuit is accidentally opened, the voltage will tend to increase so as to maintain the current. The voltage can go extremely high until it is limited by saturation of the CT.
My first choice as I said would be with the other AC wiring, all other things being equal. However, I it became apperent that by running with the AC circuits the connections may be somewhat confusing, and by running with the DC circuits the CT wiring could be arranged so as to remove all confusion that may result in a disconnect under load, I would go with the DC wiring.
I would consider any scheme that significantly reduced the possibility of confusion in the future to be the preferred method of connection.
respectfully

RE: Current Transformer leads/other wires in same conduit

The only restriction would be that code requires that any conductor in a power conduit have the correct insulation.  So if you can get your instrumentation conductors with 600V insulation then there would be no problem routing it with the 120VAC.

RE: Current Transformer leads/other wires in same conduit

I agree that either would work.  A small advantage to running the CT circuit with the DC would be that loss of either would probably disable the protection.  Putting them in separate conduits would increase the chances of losing protection from damage to one conduit.

RE: Current Transformer leads/other wires in same conduit

My concern with running the CT wiring with the AC power wiring is the chance for EMI....particularly MI. A comment was made that it is common to run CT leads in the same conduit as VT leads. This is true, but the current in the VT wiring is extremely low <100 mA for a normal electronic meter or relay connection.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources