Pile Head Fixity for 12" Pile Embedment

Pile Head Fixity for 12" Pile Embedment

(OP)
I am currently analyzing a pile cap with 12.75" diameter bored-in piles.  The embedment of the pile into the cap is 12".  Since no dowels are provided except a central core rebar, is it a valid assumption to assume that the pile is pinned?  The foundation is subject to very high lateral loads and there is a substantial difference between pinned and fixed condition.  Are there any references which might shed some light on the fixity criteria?  Any help will be appreciated.

RE: Pile Head Fixity for 12" Pile Embedment

A model of the top of pipe pile in the concrete has greater fixity than the maximum bending moment of the pipe.  I would model it as fixed against rotation and translation in all axes.

RE: Pile Head Fixity for 12" Pile Embedment

civilperson,

aleks25 did not say they were pipe piles, but rather bored piles (I'm thinking ACIP piles or small drilled shafts).

Aleks25,

Since there is no designed moment transfer, I would assume the pinned condition. However, you may want to look at a fixed condition if the deflections under the pinned condition are small.

Jeff

RE: Pile Head Fixity for 12" Pile Embedment

The maximum bending moment of drilled and cast-in-place piles is less than concrete filled pipe piles, therfore the the relative fixity is even greater for the bored piles. The moment is transfered by a couple with the top few inches of the pile being pushed one direction and the few inches above the bottom face of the cap being pushed in the other direction.  The amount of moment that can be resisted with 12" embedment is greater than the moment strength of the pile.

RE: Pile Head Fixity for 12" Pile Embedment

(OP)
"civilperson", "jdonville", thank you for your replies.  I guess there is a little confusion in nomenclature.  It is really a mini-pile with its top portion encased in steel to provide moment resistance.  I will probably model it as fixed since that gives me the most conservative pile loads (the pile group acts as the moment frame inducing tension and compression in the piles due to the lateral force alone).  And the deflection for the pinned condition is not greater than allowable

RE: Pile Head Fixity for 12" Pile Embedment

civilperson,

I think we're driving at the same point from opposite directions.

Cheers,

Jeff

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources