(OP)
I am use to using PLC 5 or control logix and I need a one shot  instrution in the old slc,it doesn't seem to support it.Is there something in the S2 file I can use?

RE: Need a ONS in a SLC 5/03

The SLC 5/03 supports the OSR inststruction which can be set up to do equivelent ONS by setting up the input conditions correctly. Of course, 2 bits are required, one as inline condition and one for the OTE. The OTE address becomes the one-shot bit in subsequent logic, the other is simply to inform the processor of the status of the OTE as the "one-scan on" address.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources