Instrumentation tagging by mechanical equipment numbers
Hi;
Does anyone have any suggestions on where I can find good guidelines or rules regarding tagging instrumentation by equipment numbers?
For example, Suppose I have a vessel: V-300
A pressure transmitter on this vessle would be PT-300, the level transmitter would be LT-300, etc.
If anyone could direct me to a web page, or if they have any suggestion on what's worked for or them and what hasn't I'd appreciate it.
We're trying to come up with some standard tagging practises and I want to make sure I've thought about it well before I start writting a spec.
--Igor
--Igor
RE: Instrumentation tagging by mechanical equipment numbers
Personally I prefer to have instruments that are associated as part of the same control loop numbered together- and then maybe throw a few others in there that are around the same piece of equipment- but not necessarily sharing the same number as that bit of equipment.
Cheers,
Daniel
dcasto: you're idea is exactly what I have in mind. Can you give me your thoughts in regards to mechanical equipment numbers, in particular what rules of thumb you've used in terms of gaps between mechanical equipment numbers, etc as well as what's worked and what hasn't worked. I believe tagging instruments (or, to be technical, tagging instrument loops) using equipment numbers is the best approach as long as the mechanical equipment tagging scheme has been well thought out. That said, if there were things that didn't work out as intended - I'd apprecaite it if you let me know what happened and in hind-sight what could have been done better.
JLSeagull: For my intents and purposes I don't think you're idea would work well. I can could already see nightmares in terms instruments changing P&IDs during the design cycle, as well as the tag number becoming too long. That said, I'm curious to know more about this type of a tagging scheme, just as information.
Cheers guys.
However we use to have a method of indiacating the location of the instrument. Examble
for transmitter we can have PT xxx. The 1st & 2nd digit to indicate the location and 3rd digit to indicate the Sl. No identification for the instrument. There can not be more than 9 Pressure Transmitter in an Area/Equipment. In case if there are more, then we can consider 4 digit instead 3 Digit.
Similar method can be followed for FT, TT, LT, PG, TG, FE etc.
KKS Kraftwerk Kennzeichen system.
This system could identify a washer on an instrument mounting bracket on a pump skid in a turbine hall in a paper mill, if you needed it to.
We've tried numbering the loops per the vessel, but as someone mentioned, you always have loops not associated with a major piece of equipment, or is shared between several.
We've also had issues with the plant changing the tank numbers after we've installed them.
Using the P&ID number also helps locate the instrument much faster.
We also use the A and B suffixes for instruments on the same loop, such as multiple Start/Stop stations for a single motor.
Instruments in the same loop should have the same number. I can't tell you how many times this is not followed. If you have a PT and a PV, they should have the same number.
______________________________________________________________________________
This is normally the space where people post something insightful.
ANSI/ISA-S5.1