Hi, is there a rule of thumb or a formula to calculate natural gas requirement of a boiler, (only known value is boiler,s output, in kW)?

RE: Boiler natural gas requirement

mechanicblues;
Is this a new boiler or an existing boiler? If it is existing, what type of fuel was originally specified for the boiler?

We have several large Power Boilers that were retrofitted to burn natural gas to avoid large deratings and one or two units that can burn 100% natural gas, if required.

RE: Boiler natural gas requirement

It is something that has to be calculated.  You have to take into account the amount of heat transferred to the water to make steam, all the losses and there are several to consider, blow down, stack losses, insulation and radiation losses, etc.  Then you will arrive at how much gas is required to produce that much KW output.

This can vary depending upon whether you have air preheat, economizers, O2 trim control; a myriad of factors.

rmw

RE: Boiler natural gas requirement

(OP)
metengr,
It is a new 3500 kw boiler. The fuel will be natural gas.

RE: Boiler natural gas requirement

If we guess a GCV of 52MJ/kg and a gross efficiency of 80% then the gas requirement can be estimated as:

(3500/1000)/(52*80)*100 which is 0.084kg/s or 670 lb/hour

regards,

athomas236

RE: Boiler natural gas requirement

(OP)
Thank you all.

RE: Boiler natural gas requirement

Another "Rule of thumb"-
3500kw output is 4375kw input at 80% gross eff.
4375kw = 14927500btu/hr. (cv1000btu/cu.ft.)

Cheers
kbs

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources