No explosions please:) class1, div. 2

No explosions please:) class1, div. 2

No explosions please:) class1, div. 2

(OP)
I have a purged enclosure in a cl.1, div. 2 location. There is a 480v 3ph feed branching off to a control xfmr and several motor starters. The cabinet was designed that upon loss of purge, everything south of the secondary side of the xfmr is to drop out, removing the potential for the contactors to operate, but leaving the 480v feed intact. In my experience, the feed is usually brought to an external contactor. Upon loss of purge, all power to the enclosure is removed. not sure which direction to go with this...

RE: No explosions please:) class1, div. 2

I'm not sure I completely understand the scenario.

Are you unable to use a UPS?

RE: No explosions please:) class1, div. 2

Hi there!
This is the part I don't get..

"In my experience, the feed is usually brought to an external contactor. Upon loss of purge, all power to the enclosure is removed. not sure which direction to go with this..."

Can you be more specific? thx
Regards

RE: No explosions please:) class1, div. 2

I should preface this by saying I'm located in Canada, so rules in other countries may be different.

From what I understand from your description, that installation would be fine up here.

Terminal blocks, lugs, and other 'non-arcing and non-sparking' devices are allowed in Cl.1, Div.2.  As long as power is cut to all unclassified bits and pieces, it's fine.  Power can still enter the box and land on a terminal strip.

Transformers are typically considered safe for Cl.1, Div.2, and there are a few manufacturers that make potted transformers that are specifically Div.2 rated.

RE: No explosions please:) class1, div. 2

Teleski,
  It appears that you are using "Type Z" pressurizaition to change the inside of the elclosure from Class I, Divison 2 to nonhazardous.  If so NFPA 496 only requires an alarm on loss of pressure.  It does not require remote power shutdown as required for "Type X" pressurization (Class I, Div 1 to nonhazardous)
Don

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources