Generator vibration cause
Generator vibration cause
(OP)
I'm looking for help with determining the cause of vibration in a generator. It is a 112mw air cooled unit attached to a gas turbine. This has been an ongoing problem for over a year. Initially we had high shaft vibration so balance moves were attempted. The shaft vibration was decreased after a number of moves but then we had casing vibration problems and axial vibration. Alignment was check and it was fine so they stiffened the generator by adding support plates from generator bearing to casing and added internal plates. This help some but over time the vibration has got worse. Recently if you change lube oil temperature or generator air temperature by a few degrees, the vibration would change. Now if you put any vars load on the generator vibration increases also. Exciter current has also increased by 50-75 amps higher than we normally see. Any ideas?





RE: Generator vibration cause
More information is needed to figure out what is really happening.
Changing lube oil temperature could indicate an oil whirl type problem, you would need to look for the appearance of vibration frequencies between 40% and 49% of running speed.
As the problem seems to be getting worse with time, you could be seeing some sort of deterioration in the rotor construction (loose wedges, short ciruit etc).
More likely though is a thermally sensitive rotor: you can balance it to a very fine tolerance either in a workshop or in-site but when you apply load, the rotor heats up and 'bends' causing sypmtoms of unbalance - run the machine again cold or at no load and you find a well balanced rotor.
What you really need to do is some basic research such as:
a) Observe vibration during a cold startup and a hot shutdown and compare using a Bode plot format
b) run the machine up from cold and monitor 1X amplitude and phase for a sufficient period of time to establish that these values reach a steady value
c) add load and repeat the monitoring of 1X amplitude and phase angles until the reach a steady value - the vector difference between c) and b) represents the thermal contribution to the overall vibration.
d) repeat b) and c) to establish repeatability (of phase angle and amplitude)
Using the data from b) and c) you could attempt a compromise balance where, instead of using vectors from cold or no load conditios, you attempt to balance out the hot or loaded 1X vectors (or go for a compromise, where you aim for acceptable vibration at both no load and on-load conditions.
It can take several hours for vibration on a generator to stabilise follwing a load change.
RE: Generator vibration cause
In any even, sounds like you need an in depth analysis of the problem as TPL described. Someone needs to take high density multichannel vibration data over both speed and load.
Where are you? Depending on location I may be able to recommend someone close by.
-The future's so bright I gotta wear shades!
RE: Generator vibration cause
RE: Generator vibration cause
Contact the Bently office (now GE) in Philly, they have one or two real good vibration analyst left there...